The problem I encounter with auto starting the Generac, by bypassing the
transfer switch and normal controls, is that the battery charger is
disconnected. Normally a 240 volt feed comes from which ever side of
the transfer switch is energized, to feed the battery charger.
There are several possible solutions. In a backup system I'm working on
now, that has a large array and grid power, that needs the transfer
switch to feed either the grid or the generator into the Sunny Islands,
I've used a different method.
The sensor and battery charging wires are removed from the 240 volt grid
feed terminals, and fed through the protected loads panel. This circuit
is broken by the generator starting relay on the master Sunny Island.
This is somewhat simplified, since another relay needs to open as the SI
relay closes.
This takes more power to operate, but the starter battery will stay
charged, and the generator will auto start on inverter commands. The
transfer switch works normally.
This would be less feasible with a small, off-grid system. The best
solution is to get an Onan, or possibly a Coleman.
Drake
> What I have done for off grid use is to cut 1 wire going to the AUTO
> side of the switch (a DPDT), install a 12 volt relay n/o contacts in
> series with that wire, then leave the switch in AUTO. When the Outback
> calls for generator, the relay closes and the generator takes over like
> you put it in AUTO. This solution leaves the MAN and OFF position for
> local control. It has worked for me on many Generacs. Of course, this
> will not work with line voltage present.
>
>
>
> Larry Crutcher
> Starlight Solar
> Yuma, AZ
> Renewable Energy Products Powered by STARLIGHT
- - - -
Hosted by Home Power magazine
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at re-wrenches.org
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
More information about the RE-Wrenches
mailing list