Outback and gensets [RE-wrenches]
William Miller
wrmiller at charter.net
Wed Sep 5 10:24:12 EDT 2007
<x-flowed>
Jeff:
The problem is with the lack of "generator support". The term does not
have anything to do with generator starting. Generator support is a
feature wherein an inverter system can synchronize with and assist a
generator in powering loads greater than the generator's capability. The
SW can do it, the Outback can not.
This is a damn good reason not to purchase Outback if your loads will ever
exceed the capability of your generator. The generator will bog down and
the inverters will release the generator input. The generator will speed
up and then the inverters will reconnect. Repeat continuously.
I'd wait for the XW. With a system this size, order a pair just for
evaluation.
William Miller
At 01:04 PM 9/4/2007, Jeff Oldham wrote:
>I'm about to embark on two very large o-t-g genset/inverter projects, one
>w/28 inverters and a modest 16kW PV array and the other w/10 inverters and
>no PV for now. These both need to rely on genset interface and I have not
>got a handle on the Outback genset interface issues that some have spoke
>of. Please enlighten me before I get in too deep, these are both outside
>of the U.S. and very remote so any "small" issue is really a very big
>issue. I've yet to experience any issues so far w/Outback and gensets but
>I tend to not do many fully automated systems w/auto start/stop and perfer
>the human interaction and logic.
>Much thanks!
>-jeff o.
- - - -
Hosted by Home Power magazine
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael_welch at sbcglobal.net
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
</x-flowed>
More information about the RE-Wrenches
mailing list