Outback and gensets was: Selecting an inverter/battery system [RE-wrenches]
Walt Ratterman
wratterman at SunEnergyPower.com
Wed Sep 5 06:22:44 EDT 2007
Jeff:
Walt Ratterman here.
I have done many Outback hybrid systems with generators and all of them
are in very remote areas. I would be glad to share with you what I have
learned.
I am in route back to the states now, and if you want we can discuss
these issues over the phone, but some basic principles are:
The generators should not be undersized.
If you are using large, three phase generators, you should see if it
works to make the Outback system three phase as well - balances out the
charging load on the generator much better, and works well.
Be sure not to get a cheap generator, or a "standby" generator.
I simply refuse to do any automatic start systems anymore. Even if the
generator controls are great, and everything seems like it will work, I
will not do it. These remote systems need to have operators who are
interested and know that the systems require constant attention.
Instead of auto-start, I use the aux relay to (a) light a light in a
prominent location to indicate that the system thinks the batteries need
charging soon, and (b) sound a loud, obnoxious horn. I have it so the
horn can be silenced for 6 hours, but the light can will not go out
until the system is no longer calling for a charge.
I set all of the battery protection set points considerably higher (more
conservative) than the factory defaults.
And then......lots and lots and lots of training.
Be glad to go over more with you off line. Just did a bunch of
hospitals - some solar some shitty grid UPS systems, all over Rwanda....
See ya,
Walt
-----Original Message-----
From: Jeff Oldham [mailto:starpower4u at juno.com]
Sent: Tuesday, September 04, 2007 1:05 PM
To: RE-wrenches at topica.com
Subject: Outback and gensets was: Selecting an inverter/battery system
[RE-wrenches] [R
I'm about to embark on two very large o-t-g genset/inverter projects,
one w/28 inverters and a modest 16kW PV array and the other w/10
inverters and no PV for now. These both need to rely on genset interface
and I have not got a handle on the Outback genset interface issues that
some have spoke of. Please enlighten me before I get in too deep, these
are both outside of the U.S. and very remote so any "small" issue is
really a very big issue. I've yet to experience any issues so far
w/Outback and gensets but I tend to not do many fully automated systems
w/auto start/stop and perfer the human interaction and logic.
Much thanks!
-jeff o.
>From the Solar, Wind and Hydro powered office of Jeff
Oldham/Regenerative SOLutions
_____________________________________________________________
Click here and choose from thousands of high quality used cars.
http://3rdpartyoffers.juno.com/TGL2111/fc/Ioyw6iigeYW5fGM1Zzx984GKUA7gW7
NTO6cOKAlUss1j9nkLu2ZVU6/
[Non-text portions of this message have been removed]
- - - -
Hosted by Home Power magazine
To send a message: RE-wrenches at topica.com
Archive of previous messages:
http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address:
www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Moderator: michael.welch at homepower.com
__________ NOD32 2505 (20070904) Information __________
This message was checked by NOD32 antivirus system.
http://www.eset.com
- - - -
Hosted by Home Power magazine
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael_welch at sbcglobal.net
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
More information about the RE-Wrenches
mailing list