We just started using Magnum Inverters. Overall we have been pleased  
with them. The sine wave is noticablly cleaner than Outback, the  
surge is better than their very extensive ratings, the wiring is much  
nicer than the "you spoke, we listened" Outback nightmare AC  
compartment, but the no load draw on the Magnums is ridiculous. Their  
literature says 2 amps @ 24 volts which is about what your  
measurements confirm. That's enough daily energy draw to run a  
refrigerator.  We're still not sure how to deal with it, I already  
had problems with the no load draw of the Outbacks compared to the  
good old DR inverters (only 10 watts on, 1 watt search)
Almost 1200 watt hours/ day is too much to take for smaller systems  
(under 1000 watts)

Ray


On Aug 24, 2007, at 1:18 PM, David Palumbo, Independent Power & Light  
wrote:

>
> Bob,
>
> I have liked some aspects of the Magnum and have been disappointed  
> with
> others.
>
> No load power draw with inverter (MS2812) on and AC breakers off =  
> 43 watts
> vs Out Back at 20 watts.
> Magnum's literature claims 25 watts no load.
>
> Also, I find that the search mode does not work as well as the Out  
> Back. I
> can not get this MS2812 to go into search at anything less than  
> 20w, even
> with the AC breakers all off. The power savings in search mode are  
> not great
> either (13.5w on 50w setting, 27w on the 30w search setting, and  
> 36w at the
> 20w setting). All of these numbers are read from a reliable  
> TriMetric meter
> and have been checked and double checked.
>
> These are tough numbers to ignore for off grid situations where  
> efficiency
> is highly valued.
>
> Dave
>
>
> -----Original Message-----
> From: Bob Ellison [mailto:reellison at gmail.com]
> Sent: Friday, August 24, 2007 2:00 PM
> To: RE-wrenches at topica.com
> Subject: Re: generator to use with Trace DR2424 [RE-wrenches]
>
>
> Home depot has some Subaru powered (10 HP OHC engines (belt drive  
> cam) ).
> Built by Coleman in the 5250 watt range that seem to be fairly good,
> just peak the rpm's a little.Good on fuel and seem to hold up engine
> wise. No problem with the generators at this point either.They are in
> the $600.00 range. I know people running them 6 hours a day with no
> problems in over a year. A balancing transformer really helps to even
> things out.
>
> Instead of a DR look at the Magnums, they have the best charger I have
> seen. The 4024 will charge better than 100 amps and the mod sine have
> the same charger.
>
> Bob
>
> On 8/24/07, Windy Dankoff <windydankoff at mac.com> wrote:
>>
>> Wrenches
>>
>> I'm advising an old customer who needs to add a backup generator to
>> cover loads added by a renter. Intending to use the DR2424 for backup
>> charging, can anyone recommend a relatively inexpensive generator,
>> likely to be locally available, that seems to provide the peak
>> voltage that the DR needs for good performance?
>>
>> Thanks
>> Windy
>> Santa Fe, NM
>>
>>
>> - - - -
>> Hosted by Home Power magazine
>>
>> To send a message: RE-wrenches at topica.com
>>
>> Archive of previous messages:
> http://lists.topica.com/lists/RE-wrenches/read
>>
>> List rules & how to change your email address:
> www.mrsharkey.com/wrenches/etiquette.php
>>
>> Check out participant bios: www.mrsharkey.com/wrenches/
>>
>> Moderator: michael.welch at homepower.com
>>
>>
>
>
> - - - -
> Hosted by Home Power magazine
>
> To send a message: RE-wrenches at topica.com
>
> Archive of previous messages: http://lists.topica.com/lists/RE- 
> wrenches/read
>
> List rules & how to change your email address: www.mrsharkey.com/ 
> wrenches/etiquette.php
>
> Check out participant bios: www.mrsharkey.com/wrenches/
>
> Moderator: michael.welch at homepower.com
>
>

R. Walters
Solarray.com
NABCEP # 04170442	




--
[Non-text portions of this message have been removed]


- - - -
Hosted by Home Power magazine

To send a message: RE-wrenches at topica.com

Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read

List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php

Check out participant bios: www.mrsharkey.com/wrenches/

Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael_welch at sbcglobal.net

EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com

For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------


</x-flowed>


More information about the RE-Wrenches mailing list