Efficient inverters vs. Load Segregation [RE-wrenches]
Jim Easton
jeaston at ucsd.edu
Wed Aug 8 18:39:35 EDT 2007
<x-flowed>
Depending on constraints, you might consider dividing up your loads, so that
the large load(s) are on large inverter(s) de-energized when not needed,
while loads that need to be constantly energized are on smaller inverter(s).
Jim Easton, PE
(E 11974)
4364 Bonita Road, No. 166
Bonita, CA 91902-1421
Tel: 858-527-0240
Fax: 619-470-8616
----- Original Message -----
From: "troy" <taharvey at heliocentric.org>
To: <RE-wrenches at topica.com>
Sent: Wednesday, August 08, 2007 12:34 AM
Subject: Efficient inverters for stand alone power systems? [RE-wrenches]
>
> I'm trying to find an efficient inverter for stand alone power systems.
>
> It seems that in the grid-tied boom, that nobody (?) has really
> addressed the fundamental problem with stand-alone inverters: efficiency
> at low power draw. Analyzing a couple of stand alone residences & small
> office applications, the *typical* power draw is quite small. You still
> need peaking performance for the occasional surge requirement, but 80% of
> the time the base load may be 100-200 watts or even less.
>
> Given the Outback Inverters as an example (a favorite of many off- grid
> designers), the weighted average efficiency is only around 75% or so for
> these applications. The most insidious thing is, as you improve the
> efficiency of the base load appliances, efficiency drops further
> (approaching zero). So for example if only one 40 watt computer is
> running the efficiency is only 40%.
>
> Obviously the problem has to do with the fact you are running against the
> quiescent current requirements of the inverter controller (which should
> be only a small fraction of a watt) and switching losses (the dominant
> issue I'd guess). But this has been addressed in switched converters long
> ago with by reducing switch frequency and/or transitioning to PFM at low
> load. We've designed power converters that are 95% efficient down to
> fractions of a watt. The point is, it should be feasible to design an
> inverter that is efficient down into the few watt range (and lower).
>
> I'd like to hear if there are any multi kW inverters (ie 2-5 kW) out
> there that are efficient down to low power draws (tens of watts) . And I
> wouldn't mind hearing any commentary from inverter manufacturers on the
> subject.
>
> Thanks,
>
> Troy Harvey
> -------------------
> Heliocentric, LLC
>
>
> - - - -
> Hosted by Home Power magazine
>
> To send a message: RE-wrenches at topica.com
>
> Archive of previous messages:
> http://lists.topica.com/lists/RE-wrenches/read
>
> List rules & how to change your email address:
> www.mrsharkey.com/wrenches/etiquette.php
>
> Check out participant bios: www.mrsharkey.com/wrenches/
>
> Moderator: michael.welch at homepower.com
>
>
- - - -
Hosted by Home Power magazine
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael_welch at sbcglobal.net
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
</x-flowed>
More information about the RE-Wrenches
mailing list