SQFlex questions [RE-wrenches]
Phil Undercuffler
p.undercuffler at conergy.us
Tue Aug 7 16:23:52 EDT 2007
Allan,
While I haven't heard of any problems related to running the SQFlex from
a GFCI protected outlet, you don't need to hardwire the pump to avoid
this concern.
NEC 210.8(A) Exception #2 allows a single receptacle for an appliance
located within dedicated space that, in normal use, is not easily moved
from one place to another and that is cord-and-plug connected.
Therefore, you can install a non-GFCI protected outlet for powering the
pump.
One caveat: you can't then use that outlet to count towards the
required dwelling receptacle outlets.
------------------------------------------------------------
Please note new phone extension!
Phil Undercuffler
Technical Services Manager
Conergy, Inc.
1730 Camino Carlos Rey Suite 103
Santa Fe NM 87507 USA
Office | 505.473.3800 x4841
Fax | 505.473.3830
www.conergy.us
------------------------------------------------------------
-----Original Message-----
From: Allan Sindelar [mailto:allan at positiveenergysolar.com]
Sent: Tuesday, August 07, 2007 12:21 PM
To: New wrenches posting
Cc: brad at aeesolar.com
Subject: SQFlex questions [RE-wrenches]
Wrenches,
A customer has an SQFlex pump that is problematic. He is using the CU200
controller, the unit designed for RE input, primarily array-direct, but
is
running it off of his 49Vnom battery bank, with a float switch to
control
operation about once/week. His ongoing problem, in his own words, "is
that
the control unit problem behavior only occurs when the well pump is not
running and the control unit has been sitting there for a couple of days
idle (the well pump only runs about once a week). All communication with
Grundfos have been useless on this subject because they only talk about
when
the well pump is running. They give me wattage requirements while the
pump
is running, etc. And I tell them my
problem has nothing to do with the well pump running. The pump has run
once
a week for nearly a year and never failed. And the control unit has
never
failed just before, during or right after a well pump run. The control
unit
has no problems idle for a few days (that is, the display will properly
show
the three zeroes 0.00 as it should). After a few days it fails and the
entire display goes blank and contrary to what Larry Seitter (at
Grundfos
tech support) says,
cycling the ON/OFF switch does not work. You have to cut all power to
the
unit and then turn it back on again. The unit will then display 0.00 and
the
pump will run without problems until the next control unit failure,
usually
after a few idle days or sometimes closer to a week but it will fail."
My questions, please:
1. Has anyone else set up an SQFlex in this manner; that is, DC battery
power to the pump, using a CU200 control unit and remote switch? If so,
have
you seen this problem?
2. I could use an MDI DC contactor with float switch coil control to run
the
pump off of DC or inverted AC, but the customer wants to keep the CU200
controller in the system for its wattage display and error code
functions. I
have been told that the CU200 may be supplied with either (30+ volts) DC
or
(90+ volts) AC power. Has anyone run AC power through a CU200?
3. Has anyone run an SQFlex on AC power through a GFCI, and if so, did
it
work? Brad Bassett of AEE has reported that the pump won't work through
a
GFCI - Brad, can you elaborate? And if I run it through AC from the
inverter, is hardwiring the pump a simple, Code-compliant method of
avoiding
the GFCI in a damp location (the pump pit)?
Thank you,
Allan at Positive Energy
- - - -
Hosted by Home Power magazine
To send a message: RE-wrenches at topica.com
Archive of previous messages:
http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address:
www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Moderator: michael.welch at homepower.com
- - - -
Hosted by Home Power magazine
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael_welch at sbcglobal.net
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
More information about the RE-Wrenches
mailing list