We're experiencing something similar with Fronius inverters in various
locations throughout Colorado.  Similar story as far as the utility goes
in that they're claiming everything is fine, while we're consistently
measuring voltages outside of the inverters' tolerable window (130-140
VAC).  We've tried our own measurement methods as well as the utility's,
but Fronius says we need more sophisticated equipment that can log and
measure voltage multiple times per second (one of our devices only
measured every few seconds).  We're expecting to get the appropriate
piece of equipment within the next few weeks (Fronius tells us its
expensive - around $6k) and I'd be happy to share with you information
about the equipment as well as how our test results go.  Please feel
free to contact me after 2-3 weeks and we'll hopefully have the issue
wrapped up by then.

Best Regards,

Blake Jones
Co-Owner, President
NABCEP and CoSEIA certified PV installer

Namaste Solar Electric
2639 Spruce St.
Boulder, CO 80302
303.447.0300 x203 direct
303.443.8855 fax
www.namastesolar.com 




-----Original Message-----
From: Drake Chamberlin [mailto:Drake.Chamberlin at redwoodalliance.org] 
Sent: Thursday, June 28, 2007 5:13 PM
To: RE-wrenches at topica.com
Subject: Grid fluctuations [RE-wrenches]


Hi Wrenches,

We have a Sunny Boy that keeps shutting down for periods, then 
restarting.  We have measured grid voltage of 137 VAC per phase, and 
think that is the problem.  The utility company is claiming that the 
grid is fine.

Does anyone know where we can get a recording voltmeter to put on the 
grid.  There is no Internet access at the location.  We just want to 
be able to record the voltage over time.  We suspect that their may 
be short term spikes, which we would like to catch.

Thanks,

Drake 


- - - -
Hosted by Home Power magazine

To send a message: RE-wrenches at topica.com

Archive of previous messages:
http://lists.topica.com/lists/RE-wrenches/read

List rules & how to change your email address:
www.mrsharkey.com/wrenches/etiquette.php

Check out participant bios: www.mrsharkey.com/wrenches/

Moderator: michael.welch at homepower.com


- - - -
Hosted by Home Power magazine

To send a message: RE-wrenches at topica.com

Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read

List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php

Check out participant bios: www.mrsharkey.com/wrenches/

Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael_welch at sbcglobal.net

EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com

For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------






More information about the RE-Wrenches mailing list