Geoff,

On new buildings, in the specifications under Div. 16, the electrical 
engineer will sometimes call for 3 phase legs to be balanced within __%.
I think it is 5 % but I'm not sure.  This is refering to the loads of 
course, but it is the same principle.  Acutally the PV is a negative 
load from that point of view.  Since loads are always changing it is 
just a general guideline.

If you put an amprobe on the 400 amp main and found Phase A to be 10% 
higher than Phases B and C and you hooked up to Phase B and C with 15% 
input of PV then the resulting 25% variance may be off some concern.  
You would want to hook up to AB or AC to level things out a bit.

I havnen't found it to be a problem so far on 600 amp services with 
12kw.  The 2 6kw inverters were combined in a panel so that only 1 phase 
overlapped when it was fed into the system.

Steve Johnson
LightWave Solar Electric
Nashville, Tennessee


- - - -
Hosted by Home Power magazine

To send a message: RE-wrenches at topica.com

Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read

List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php

Check out participant bios: www.mrsharkey.com/wrenches/

Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael_welch at sbcglobal.net

EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com

For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------



More information about the RE-Wrenches mailing list