Unfused AC Disconnects with neutral terminal [RE-wrenches]
Bob-O Schultze, Electron Connection
econnect at snowcrest.net
Tue May 22 17:27:06 EDT 2007
<x-flowed>
Hiya Ron,
We pull the neutral straight through and deadhead it off in the
gutter below the inverter or wherever. Since the ac neutral is a
grounded conductor, there is no reason you would ever want to switch
it or need to bring it into an external safety switch. Hot legs in,
hot legs out and an equipment ground wire. Done. The Sq.D DU221RB
and 222RB work for me.
Good Luck, Bob-O
On May 22, 2007, at 1:21 PM, Ron Stephan wrote:
>
>
> Hi all,
> I need some advice on AC disconnects for residential systems. The
> utility in New York requires an lockable AC disconnect close to the
> meter. Even if a lot of the inverters now come with integrated
> disconnects, depending on the inverter location we often need an
> additional AC disconnect.
>
> With all kinds of inverters coming out with a neutral for IEEE 1547
> compliance, I have a hard time finding unfused, 120/240Vac, 30A or 60A
> disconnects with a neutral terminal. We been using a lot of SquareD's
> DU221 and DU222 but there is no neutral terminal available for
> those. I
> been thinking of just pulling the neutral straight though the
> disconnect
> (continuous from the inverter to the breaker ) without attaching to a
> neutral terminal but I am not sure that meets the code.
>
> Does anybody has a better idea? Are there disconnects out there that
> meet the purpose?
>
> Thanks,
> Ron
>
> Ron Stephan
> Solar Energy Systems, LLC
> 1205 Manhattan Avenue
> Suite 1210
> Brooklyn, NY 11222
>
> www.solarEsystems.com
>
> ph. 718.389.1545 ext. 12
> fx. 718.389.2820
- - - -
Hosted by Home Power magazine
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael_welch at sbcglobal.net
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
</x-flowed>