Gents,

I think there's a basic misunderstanding here. Correct me if I'm wrong
please Todd. 

I have it direct from two of the principals at Outback that the grid-tie
version will stop battery charging if AC input voltage or frequency drifts
outside the tight IEEE standards, but it WILL NOT disconnect from the AC
source unless voltage drops below about 90 volts or the frequency gets more
than 5 hz out. So under generator support we might lose battery charging for
5 minutes when the well pump starts (which might not be such a bad thing),
but the main AC contactor stays engaged and the generator will continue
running the loads directly. 

Christopher, can you verify this? I heard it from Marty and Roy last week. 

If true, this doesn't seem like such a big deal. It might take a bit longer
to charge the batteries, but it isn't like customers are going to be stuck
without power unless they've got a really nasty generator.

Cheers,
Doug Pratt
DC Power Systems


-----Original Message-----
From: Todd Cory, Mt. Shasta Energy Services 

Jeff,

The big issue here is that the GVFX inverter very likely will not be 
able to use the generator power. Some inverter generators are stable 
enough for the inverter to accept. This makes the other legitimate 
issues you mentioned moot IMO.

Todd


Jeff Yago wrote:

>Chris:
>
>Thanks for your heads up on new things to come at Outback.   Hint - This is
a tough group, if anyone  stays off line for over a week we start trashing
them!  
>
>The big issue you could clear up is when using the Outback in grid sell
mode with batteries, MATE, and a back-up generator.  You have read the many
rants about not having an AC2 set of terminals to connect a generator to the
inverter in addition to the grid on AC1 and I will not rehash that one.  
>
>Of course the work-around is using a separate automatic transfer switch
with the generator, which will switch to the generator when there is a loss
of grid power.  However, my original concern with this on a system we are
designing right now is what happens when the Outback "sees" a different AC
source.  Its input is being switched from a AC source the inverter was
programmed to sell to and not control, to a source that it should not sell
to and should control (low battery generator start/stop).
>
>When I first posted the question, there were many who indicated the
home-owner has to manually switch settings on the MATE every time there is a
power outage.   Please resolve this once and for all.   We have a 12 kW
generator and transfer switch ahead of the inverter, since it has a higher
output than a single GVFX inverter can handle, so we can also supply several
larger non-inverter loads like a clothes washer and gas dryer.   When using
a GVFX3648 inverter with batteries and a MATE, programmed for SELL mode to
the grid, exactly what happens if there is a power outage and a generator
starts supplying power to the inverter instead of the grid?   
>
>1.  Does the inverter shut down or just dis-connect from grid?
>
>2.  If the inverter "sees" the generator come on line, will it think its
the grid and try to sell to the generator?
>
>3.  Will the inverter charge the batteries as soon as the generator comes
on line or will owner need to re-program MATE settings?
>
>4.  Will the MATE start and stop the generator as needed to maintain the
batteries while also programmed for "sell" mode to the grid?
>
>5.  Since the inverter and batteries can handle the critical loads until
the grid is restored, how best to inter-face with the
>    automatic transfer switch so the generator does not start until needed
for battery charging while still programmed for SELL mode?  
>
> Again, the issue is how can this be done without the home-owner having to
re-program the MATE every time there is switch from grid sell to  generator
back-up.
>
>Thanks,
>
>Jeff Yago
>


- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read

List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php

Check out participant bios: www.mrsharkey.com/wrenches/

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com

EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com

For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------








More information about the RE-Wrenches mailing list