Grid sell with Outback, solar,and generator [RE-wrenches]

Darryl Thayer daryl_solar at yahoo.com
Wed Apr 25 07:43:42 EDT 2007


Jeff is this a 48 volt battery system?
     is the generator to serve only the critical loads
or all loads?  or critical and gen special loads?  Is
it important that the gen cycle back and forth between
inverter and gen (auto or manual start) or once the
batterys are down they can wait until grid gets back
on line?

Daryl

--- Jeff Yago <jryago at netscape.com> wrote:

> 
> I know this thread has just about been beat to
> death, but I wanted to see if I could summarize
> everyones thoughts as we are getting ready to
> install this exact same system.
> 
> Battery-based Outback Grid-tie Inverter system with
> about 2 kW solar and a 12 kW backup generator. 
> Client wants to sell any excess solar power as they
> are gone most of the week, but area has lots of
> power outages so generator backup is important. 
> Since no AC1 and AC2 inputs, the easiest route is to
> set up inverter as grid-tie, and use any excess
> solar for net metering.   Install a standard AC
> generator transfer switch ahead of inverter and its
> emergency panel loads.
> 
> However, as everyone has already pointed out, the
> Outback will not handle this change properly without
> being told the input power supply is now a generator
> and not the grid.  How big a deal is this
> change-over for the client if they have a Mate?  Can
> this change-over be simplified or pre-programmed to
> only require a single command?  What is easiest
> program settings to stay with that reduces these
> control issues if the generator will only be used
> during an extended power outage?
> 
> Thanks,
> 
> Jeff Yago
> 
>
_____________________________________________________________
> Netscape.  Just the Net You Need.
> 
> 
> - - - -
> To send a message: RE-wrenches at topica.com
> 
> Archive of previous messages:
> http://lists.topica.com/lists/RE-wrenches/read
> 
> List rules & how to change your email address:
> www.mrsharkey.com/wrenches/etiquette.php
> 
> Check out participant bios:
> www.mrsharkey.com/wrenches/
> 
> Hosted by Home Power magazine
> 
> Moderator: michael.welch at homepower.com
>
> 
> 


__________________________________________________
Do You Yahoo!?
Tired of spam?  Yahoo! Mail has the best spam protection around 
http://mail.yahoo.com 


- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read

List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php

Check out participant bios: www.mrsharkey.com/wrenches/

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com

EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com

For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------



More information about the RE-Wrenches mailing list