sharing conduit [RE-wrenches]
Bill Brooks
bill at brooksolar.com
Thu Apr 19 01:52:26 EDT 2007
Nicholas,
How about running a listed cable assembly (MC) in the 2". I believe hat
gives you the barrier you are looking for since the power conductors are
enclosed in the cable assembly. I would clear it with your local
jurisdiction before I made any assumptions, however.
Bill Brooks, PE
Brooks Engineering
873 Kells Circle
Vacaville, CA 95688
office and mobile phone: 707-332-0761
fax:707-451-7739
email: billbrooks7 at yahoo.com
web: www.brooksolar.com
Ecclesiastes 11:7 Light is sweet, and it pleases the eyes to see the sun.
> -----Original Message-----
> From: Nicholas Ponzio [mailto:wrench at vtsolar.com]
> Sent: Wednesday, April 18, 2007 7:43 AM
> To: RE-wrenches at topica.com
> Subject: sharing conduit [RE-wrenches]
>
>
> Is there a way to legally run AC inverter output through a conduit (2"
> PVC)
> that already has co-axial TV cable in it?
>
> My reading of the code (see below) suggests that we need a "permanent
> barrier or listed divider." What constitutes a divider?
>
> Thanks in advance for any suggestions or insights.
>
>
>
> * NEC Reference:
> 800.113.A.1.5.c Communications conductors shall not be placed in any
> raceway, compartment, outlet box, junction box, or similar fitting with
> conductors of electric light, power, Class 1, non-power-limited fire
> alarm,
> or medium power network-powered broadband communications circuits.
>
> Exception No. 1: Where all of the conductors of electric light, power,
> Class
> 1, non-power-limited fire alarm, and medium power network-powered
> broadband
> communications circuits are separated from all of the conductors of
> communications circuits by a permanent barrier or listed divider.
>
>
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
More information about the RE-Wrenches
mailing list