Grid tie with Diesels? [RE-wrenches]
Darryl Thayer
daryl_solar at yahoo.com
Wed Apr 11 19:55:59 EDT 2007
Hi Steve
I have not delt with a diesel-solar grid this big, so
take what I say with a grain of salt. I have delt with
solar this big and battery systems up to only 3000 AH,
you will be bigger than this.
But it seems why have a 500kW genset and a 225 genset,
and only a solar 60 kW? How does the 60 kW carry the
load? At night only? A better description of the load
would be helpful. Please note if the solar during the
day is directly grid tied, there is a reduction in
diesel fuel usuage. BSFC (brake specific fuel
consumption) on a Diesel is rather flat over a large
power range. (means the fuel consumption is dependent
upon the power delivered mostly, this is unlike SI
engines)
If the 225kW can carry the load why not have a second
225 kW as a backup? If the Diesel is the core for the
3 phase power, several PV inverters can support the
Core, but it seems supporting the core is very
different from creating the core with the inverters.
Battery life:
For battery cycling 50% might be too deep for daily
cycles, I think that 70% or 80% SOC or 30 or 20%DOD
would give longer Battery life. Further as the
batteries age, that 50% DOD is going to get hardeer
and harder to reach. The batteries will recieve a lot
of heat in this process.
I think that a repetitive discharge rate of up to C/10
will lead to long battery life. Furthermore
batteries need to be charged at a slower rate. Where
C/10 from 50% DOD to 30% DOD is ok and C/20 from 30 to
10% the last 10% should be charged at about C/50. The
batteries need to be taper charged and as they reach
full charge. This means the charge rate must be slow
near full charge. At 50% DOD it might take 12 hours
to recharge and let the batteries cool.
Darryl
--- Steve Johnson <stevejohnson at comcast.net> wrote:
>
> Geof,
> I'm budgeting a system like this too, but with a 500
> kw diesel genset
> (proposed by others). This genset would be transfer
> switched to another
> system backed up with a 225 kw diesel which is in
> tandem with some
> inverters with batteries and some grid-tied and AC
> coupled with PV.
> Maybe 60 kw PV.
> When the 225 diesel generator is on it would run
> close to full bore, say
> 80% or so, charging batteries and running the grid.
> When batteries get
> charged it shuts off.
> The grid tied PV and battery/inverter systems would
> operate the system
> quietly as long as capable. When batteries get to
> 50% the 225 diesel
> kicks in and supplies grid while charging batteries,
> then shuts off
> again. This is just a preliminary design and no I
> haven't done a
> successful (or unsuccessful) project like this
> before.
>
> The battery inverters would have to set the "tone"
> for the grid as they
> are the only thing always available. But if they
> set the grid standard
> then how can the genset match it? This is where I
> am stuck. But then it
> is late . . .
>
>
> Steve Johnson
> LightWave Solar Electric
>
____________________________________________________________________________________
No need to miss a message. Get email on-the-go
with Yahoo! Mail for Mobile. Get started.
http://mobile.yahoo.com/mail
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
More information about the RE-Wrenches
mailing list