Tracker with Outback PSPV [RE-wrenches]
Brian Teitelbaum
brian at aeesolar.com
Wed Mar 14 20:56:46 EDT 2007
Bill,
I think that your inspector is full of s*** (don't tell him that though.
Bring him doughnuts instead). The tracker is not part of the power producing
equipment. It is only an electrical appliance (load) and is not required to
be UL listed. Neither is the power supply for the tracker. It's also a load.
You can plug in a non UL TV, toaster, or other load (not that I recommend
buying non-UL Listed appliances) and it's not any of the inspector's
business.
By the way, none of the equipment that you see on the utility's power pole,
or at their substation or power plant, is required to be UL Listed.
I can understand him not liking the power supply in the PSPV. Mixing AC and
DC in the same JB is frowned upon. Put it in a separate 3R box.
My $0.02
Brian Teitelbaum
AEE Solar
-----Original Message-----
From: Bill Hoffer [mailto:Sunergy at charter.net]
Sent: Wednesday, March 14, 2007 3:59 PM
To: RE-wrenches at topica.com
Subject: Tracker with Outback PSPV [RE-wrenches]
I am being told by my local inspector that I cannot have my AC/DC power
supply for my Wattsun tracker in my PSPV combiner box from Outback (ref
NEC 312.8). Outback manual PN900-0021-1 does state that it can also be
used as an enclosure for AC Components up to 240VDC. I am only using 2
circuits for my PV leaving plenty of space for the power supply. He is
also saying that the tracker is not listed and therefore I cannot use it
at all! Gee wonder how Wattsun can stay in business! Anyone have any
experience with this situation? Thanks!
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
More information about the RE-Wrenches
mailing list