Class T fuse source request [RE-wrenches]

Ray Walters walters at taosnet.com
Tue Feb 13 20:05:26 EST 2007


<x-flowed>

We always used the rule of thumb from the Ananda power centers, Trace, 
etc.: 2/0 cable gets a 200A T fuse or 175 A breaker, 4/0 gets a 400A T 
fuse or a 250 amp breaker. If you look at the trip curves it makes more 
sense. TheT fuses definitely trip faster (lower current) than the Heinemans.
I ordered some 300 A fuses once through Summit Electric they were over 
$50 a pop. I quit looking at the in between sizes after, and all has 
been well since.

Ray


Allan Sindelar wrote:

>Wrenches,
>What is a good wholesale source for 225A or 250A Class T fuses, of the
>bolt-on type that has been used in our industry for years? Readily-available
>sizes through PV distributors have always left a gap between 200A and 300A
>sizes. I need two only. Thank you.
>
>Allan at Positive Energy
>
>
>  
>


- - - -