William,
Here is the text from NEC 2008 690.31:
("E) Direct-Current Photovoltaic Source and Output Circuits Inside a
Building. Where direct-current
photovoltaic source or output circuits of a utility-interactive inverter
from a building-integrated or other
photovoltaic system are run inside a building or structure, they shall
be contained in metal raceways, or
metal enclosures, from the point of penetration of the surface of the
building or structure to the first
readily accessible disconnecting means. The disconnecting means shall
comply with 690.14(A) through
(D)."
It appears that there has been no change in this Article. There was an
attempt to modify to specifically allow MC cable, but that did not make
it into the new code.
Status Quo for three more years.
I use only EMT and FMC inside the building.
William Miller wrote:
>
> Friends:
>
> As you all know, the 2005 code allows for PV source conduit to enter a
> building envelope without first passing through a disconnect IF the
> conduit
> is metal. Does anyone have factual knowledge if this will change for
> 2008?
>
> William Miller
- - - -
Hosted by Home Power magazine
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at re-wrenches.org
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
More information about the RE-Wrenches
mailing list