Hi Hugh,
Nice to hear from you.
If that was the case usually the inverter would still see the AC
input although it would be outside of its connection parameters. So
it "shouldn't" shut the generator down and then restart it.
The fact that it does it on both inverters and how quickly to me
indicates a bad mate ie sending a bad set of signals.
I've seen it a number of times, and usually when I do get a mate gone
bad, resetting it doesn't seem to work. Or it might for a short
time, then will have the same problem again, so its not worth trying
and having to go back again to swap it out. I just change then out.
jay.
On Dec 4, 2007, at 12:47 PM, Hugh Piggott wrote:
>
> At 12:36 -0800 4/12/07, Jonah Liebes wrote:
>> I have not tried that. I keep the gen itself set to Auto and use
>> the mate to
>> toggle between manual and auto as needed. It is strange that the
>> gen cycling
>> occurs even when the AGS in the mate is set to manual. I hear the
>> relay
>> click so I know the FX is sending the signal- even in manual mode.
>
> I wonder what you have set for the generator size (INPUT AC2 gen),
> and whether it is overloaded. I wonder if the AC voltage drops to
> the point that the FX rejects its input, and shuts it off?
> --
> Hugh Piggott
>
> Scoraig Wind Electric
>
> http://www.scoraigwind.co.uk
>
>
> - - - -
> Hosted by Home Power magazine
>
> To send a message: RE-wrenches at topica.com
>
> Archive of previous messages: http://lists.topica.com/lists/RE-
> wrenches/read
>
> List rules & how to change your email address: www.mrsharkey.com/
> wrenches/etiquette.php
>
> Check out participant bios: www.mrsharkey.com/wrenches/
>
> Moderator: michael.welch at homepower.com
>
- - - -
Hosted by Home Power magazine
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at re-wrenches.org
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
</x-flowed>
More information about the RE-Wrenches
mailing list