Flex ware inverter bypass slide [RE-wrenches]
Christopher Freitas --- OutBack Power
cfreitas at outbackpower.com
Thu Nov 29 19:50:33 EST 2007
jay peltz wrote:
> Whats funny is that Midnite solars box's work perfectly,
Perfectly Huh? I strongly disagree - the Midnite AC bypass is not safe
or compliant with the UL standards for a System Bypass or the NEC code
because:
The AC bypass bypass slider plate does not allow you to set both circuit
breakers to the OFF position.
It also does not allow the handle of the circuit breaker to indicate
that it has tripped due to the extremely small opening for the handle in
the AC bypass slider plate.
The AC bypass slider plate also covers up the labeling on the breaker as
to the amperage and on/ off status.
I think these are serious safety issues with the Midnite product.
Christopher Freitas
OutBack Power Systems, Inc.
cfreitas @ outbackpower.com
www.outbackpower.com
Arlington WA USA
Tel 360 435 6030
- - - -