Jay,

He tried unsuccessfully to argue low voltage. I don't see any exceptions 
under 690.5 in the 2002 or 2005 codes.

John R.,

A referral to John Wiles might help in this instance?

Thanks,
Brad


jay peltz wrote:
> 
> HI Brad,
> 
> Would it fall under the low voltage section?
> 
> Or how about using a "pole".  690.5 exception 1.
> 
> jay
> 
> peltz power
> On Nov 16, 2007, at 9:41 AM, Brad Bassett wrote:
> 
> >
> > I have a customer installing SDHW systems with PV powered pumps and  
> > the
> > inspector is now saying they have to use a GFP on this 10w module when
> > installed on a dwelling! If this continues and they adopt the 2008  
> > code
> > it would have to be done for all installations. I can't find any
> > exceptions in the code to fight this (one would think common sense  
> > would
> > work). As I see it one of the breaker based GFP's is about the only
> > choice and at 0.5A trip point a dead short in a 10W module would only
> > occasionally even trip it. Any ideas?
> >
> > Brad Bassett
> > AEE Solar
> >

> >
> 



Brad Bassett


- - - -
Hosted by Home Power magazine

To send a message: RE-wrenches at topica.com

Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read

List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php

Check out participant bios: www.mrsharkey.com/wrenches/

Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at re-wrenches.org

EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com

For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------




More information about the RE-Wrenches mailing list