NEC 2008 690 changes [RE-wrenches]
Mark Frye
markf at berkeleysolar.com
Wed Nov 14 16:21:22 EST 2007
>From a source previously mentioned, a compilation of:
Changes from 2005
• 690.4(D): Specified that equipment be identified and listed for the
application.
• 690.5: Revised to require all grounded dc PV arrays be provided with
ground-fault protection unless they meet either of the conditions in the
two exceptions.
• 690.5(B): Added requirement on permitted means to isolate faulted
circuits.
• 690.5(C): Provided specific wording for warning label required to be
factory- or field-installed on the inverter.
• 690.10(A): Clarified that the ac output of a stand-alone inverter may
be less than the calculated load, provided the output is adequate to
supply the largest single utilization equipment.
• 690.13: Specified that a switch, circuit breaker, or other device,
unless part of a ground-fault detection system, cannot be installed in
the grounded conductor if it results in the grounded conductor’s
becoming ungrounded and energized.
• 690.31(A): Revised to require readily accessible conductors operating
at over 30 volts to be installed raceways.
• 690.31(B): Revised to require use of either USE-2 or listed and
labeled photovoltaic (PV) wire.
• 690.31(F): Added section to provide termination requirements for
flexible, fine-stranded cables.
• 690.33(C): Added requirement for connectors that are readily
accessible and used with systems operating at over 30 volts to require a
tool for opening.
• 690.43: Clarified that an equipment grounding conductor is required
between the PV array and other equipment, and added requirements for
devices used to ground metal frames of PV modules.
• 690.45: Revised requirement on size of equipment grounding conductors
to at least 14 AWG.
• 690.46: Added requirement for physical protection of equipment
grounding conductors smaller than 6 AWG.
• 690.47(C): Specified the means of grounding and bonding PV systems
with ac and dc grounding and bonding requirements.
• 690.47(D): Added section to provide requirements for grounding
electrodes at ground and pole-mounted arrays.
• 690.57: Added requirement that load disconnects supplied by multiple
sources disconnect all sources when in the off position.
• 690.64: Specified that requirements apply to systems with
utility-interactive inverters.
• 690.64(B)(1) through (7): Revised to provide interconnecting
requirements for distribution equipment capable of supplying multiple
branch circuits or feeders while simultaneously connected to primary
power and one or more interactive inverters.
• 690.74: Added requirement for the use and termination of flexible
fine-stranded cables for battery interconnections.
Berkeley Solar Electric Systems
- - - -
Hosted by Home Power magazine
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at re-wrenches.org
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
More information about the RE-Wrenches
mailing list