Drake wrote:
> The new FLEXmax 80 sounds like a great product. A controller that we
> really need now (IMO) is one that can charge from a 300 to 550 volt
> array. Are the technical obstacles to producing this too great?
Its not a problem producing a MPPT controller which can step down a 300
or even 600VDC PV array to 48VDC - its just hard to do it efficiently
enough & at a low enough cost that people would buy it.
We (and others) have been working on it for years - and haven't been
successful so far with the available parts.
Also keep in mind that we also will need 300 or 600VDC rated disconnects
and GFDI systems as well - which can be done, but gets real expensive
compared to the cost of the low voltage (150VDC) circuit breakers and
GFDI systems. With the increased cost for copper and labor - perhaps it
will be economical at some point. From our calculations - its just not
economical so far.
Its also easy to forget that the FM80 is really a 4000 watt DC-DC
converter - but one that sells for $750 USD - and includes a LCD display
and full metering / data logging system and communication system. A
comparable power supply for a lab bench would be more than $2000 and a
similar 4kW PV inverter costs more like $3000 or so...
The reason we increased the output power capacity to 80 amps is that PV
modules and systems are tending to be larger - and there is less labor
and cost installing one controller versus two controllers. The FM80 is
also a perfect match for the GVFX3648 inverter - where as the old MX60
did not really allow the inverter to sell back at full power unless more
than one controller was used.
Christopher Freitas
OutBack Power Systems, Inc.
cfreitas @ outbackpower.com
www.outbackpower.com
Arlington WA USA
Tel 360 435 6030
- - - -
Hosted by Home Power magazine
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at re-wrenches.org
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
More information about the RE-Wrenches
mailing list