John Raynes wrote: "What would happen in a system with more than one XW
charge controller tied into the same DC bus? Wouldn't each controller
see the other's GFP as an external ground fault?"
Mick says: In a system with multiple XW controllers, the manual says to
remove the fuses from all the controllers except for one. I think this
is not because the other controllers would look like a ground fault but
rather the opposite: the other fuses would provide alternate links
between negative and ground so that a 1 amp GFP fuse could not be relied
upon to blow at that low value.
John wrote: "I would hope that there would be some way of
disabling the internal GFP", and Dan Rice wrote: "negative and ground
must be kept isolated so the GFP will work correctly, and probably for
the controller to work at all."
Mick says: There's nothing you can do within the charge controller
itself to disable the GFP. Regarding the recommended isolation of
negative and ground elsewhere in the system, the manual says: "Bonding
the negative to ground disables PV ground-fault protection and causes
improper unit operation." The manual says other things to discourage
this...things like "WARNING: Shock Hazard" and "NEC requirements".
In spite of these intimidating words, I suspect that the XW control
would still work normally (in a retrofit system where there's already a
negative/ground bond) except for the GFP feature. If there is a
neutral/chassis bond exterior to the XW controller, this would prevent
any voltage potential from developing across that fuse so the fuse could
never blow, but to the controller that would look just like normal
operation with no ground fault. Confirmation or refutation of this
theory would be welcomed. Not all installations require DC ground fault
protection, after all...
- - - -
Hosted by Home Power magazine
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at re-wrenches.org
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
More information about the RE-Wrenches
mailing list