solareagle wrote:
>
>
> Hello Wrenches,
> Has anyone had any experience installing Sanyo HIT panels in off grid
> applications? Because of their high voltage and VOC I think they can
> only be strung together in singles in our cold winter environment
> using an MX or Blue Sky controller. That makes it a little awkward
> for getting the best (smallest) wire size for arrays located some
> distance from the power house. Any comments?
>
> Ron Young
Hi Ron,
I install many Sanyo HIP 200BA3 panels in battery based systems. I just
put 3 on a motorhome today and I always run them parallel. The Voc of
the 200 is 68.7. Two in series is 137.4 at 77F. There is no place in the
USA that the temperature does not drop below 77 at some time during the
year. In other words: don't even think about doing it.
The Blue Sky 6024 has a zener diode set at 140 volts. It will disable
the PV input if you ever exceed maximum input voltage and the zener will
have to be replaced. No warranty for the repair. (although Rick is very
forgiving most of the time!) The MX60 will permanently log the over
voltage. Not sure what will happen but if you have a warranty issue and
they see the over voltage...
The HIP 200BA3 has 3.59 Imp. You did not mention how many modules you
are using but 4 200's with an 80' run will only have 1.65% loss (about
13 watts) using 6 gauge. Thats much better than the old days of 48 or 24
volt runs and huge wire.
Larry Crutcher
Starlight Solar
Yuma, AZ
Renewable Energy Products Powered by STARLIGHT
- - - -
Hosted by Home Power magazine
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at re-wrenches.org
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
More information about the RE-Wrenches
mailing list