Blair, I am a little slow. Are you interrupting the power supply to
the controller?
Jeff Wongstrom
Thirsty Lake Solar
On Oct 17, 2007, at 8:47 AM, blair may wrote:
>
> By installing a simple relay and controlling the 2 wires that are
> used to place the unit into auto mode you eliminate that phampton
> load. The 12 v relay coil #s 85 & 86 is controlled by your AGS
> module. This unit does't have a battery charging circuit, but does
> come w/ a ac charger that can be wired into the output circuit.
> Sent via BlackBerry by AT&T
>
> -----Original Message-----
> From: Jeff Wongstrom <thirstylake at interbel.net>
>
> Date: Wed, 17 Oct 2007 08:17:55
> To:RE-wrenches at topica.com
> Subject: Re: generator suggestions [RE-wrenches]
>
>
>
>
> We recently had a fellow ask us to hook up a 12 RES that he had
> bought from Lowes that came with an ADC 2200 controller. We were
> told that normally the RES comes with the ADC 2100 controller which
> is reprogrammable and can be programmed to power down after 1 or 48
> hours. The ADC 2200 is not reprogrammable.
>
> We were also told that the RES can be rewired for full output 120VAC
> (L1 and L3 neutral, L2 and L4 hot) but the controller needs to be
> reprogrammed accordingly, not possible with the ADC 2200.
>
> Jeff Wongstrom
> Thirsty Lake Solar
>
>
>
> On Oct 17, 2007, at 5:38 AM, Travis Creswell wrote:
>
>>
>> Hi Todd,
>>
>> We recently installed a Kohler 12 RES and couldn't be more pleased
>> with it.
>> I think the 8.5 is the same unit, just smaller. For the price the
>> 12 RES
>> was hard to beat. $3519 with free shipping from Ziler Electric.
>>
>> We installed several 12RES and they have been good units. 2-wire
>> start, able
>> to run 100% unbalanced (you can have 6kW on one phase and nothing
>> on the
>> other and they don't care), quiet and reliable.
>>
>> The main wart with these units is they have a phantom load via
>> their on
>> board controller. You used to be to pull a jumper off of the board
>> and
>> partially resolve that but the last unit we got arrived with a potted
>> controller board so there was no way to get to that jumper without
>> damaging
>> the control board. But they do everything else so well the
>> controller
>> phantom's load can be easily accepted.
>>
>> Best,
>> Travis Creswell
>> Ozark Energy Services
--
[Non-text portions of this message have been removed]
- - - -
Hosted by Home Power magazine
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at re-wrenches.org
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
</x-flowed>
More information about the RE-Wrenches
mailing list