Hi 
I am most experianced with Outback installations in
this situation.  First "earth"/ground the frames and
strtucture, and where it is feasible I run a ground
wire, to a ground rod and to the electrical system
ground.  This is run in parallel with the equipment
ground conductor.  

The array current carrying conductors are connected to
ground through an Outback or other lightning arrestor.
 I believe Outback is now requireing the use of their
arrestor on the AC side of the inverter.  I also put a
lightning arrestor on the DC side.  ALWAYS

Thanks Darryl

--- Howie Michaelson <howie at suncatchervt.com> wrote:

> 
> So if one has a roof mounted battery based system
> (and therefore the GFDI
> is required) how do folks deal with lightening
> protection issues?
> 
> Howie Michaelson
> NABCEP Certified Solar PV Installer™
> 
> Sun Catcher, LLC
> Renewable Energy Systems Sales and Service
> http://www.SunCatcherVT.com
> (cell) 802-272-0004
> (home) 802-439-6096
> 
> 
> >
> > Hi
> > If you have the GFDI used with your
> modules/system,
> > you are not allowed to ground except through the
> GFDI.
> >  That is the module frames and racking should be
> > "earthed" of course, but neither of the current
> > carrying conductors should be connected to ground
> > "earth" EXCEPT VIA GFDI circuit.  So you should
> not
> > ground the positive or negative of the battery. 
> If I
> > do not have a GFDI then I usually ground the
> negative
> > side, note if you ground the current carrying
> system
> > at the battery negative, this is the only place
> the
> > conductors should be grounded other wise you will
> have
> > parallel paths.
> > Darryl
> >
> > --- Ron Schroeder <wd8cdh at optonline.net> wrote:
> >
> >>
> >> If you have to float the system, earthing thru a
> >> spark gap will provide some
> >> protection.
> >>
> >> Ron Schroeder
> >> WD8CDH
> >> NABCEP Certified PV Installer
> >>
> >> ----- Original Message -----
> >> From: "Warren Lauzon" <windsun at wind-sun.com>
> >> To: <RE-wrenches at topica.com>
> >> Sent: Wednesday, October 03, 2007 7:18 AM
> >> Subject: Re: Earthing battery banks [RE-wrenches]
> >>
> >>
> >> >
> >> > We have been having that debate among ourselves
> >> for years :P
> >> >
> >> > Electrically it seems like it is 50-50,
> sometimes
> >> better to float.  But
> >> > lightning protection with a floating system can
> be
> >> a real problem, and
> >> > with ungrounded batteries stuff can flash
> around
> >> all over looking for a
> >> > path to ground, even on nearby strikes.
> >> >
> >> > So 98% of the time we opt for a negative ground
> >> >
> >> >
> >>
> >
>
..................................................................................................
> >> > Northern Arizona Wind & Sun - Electricity From
> The
> >> Sun
> >> >
> >>
> >
>
..................................................................................................
> >> > ----- Original Message -----
> >> > From: "Carl Emerson, Free Power Ltd."
> >> <freepower at freepower.co.nz>
> >> > To: <RE-wrenches at topica.com>
> >> > Sent: Tuesday, October 02, 2007 5:54 PM
> >> > Subject: Earthing battery banks [RE-wrenches]
> >> >
> >> >
> >> >>
> >> >> Hi Group,
> >> >>
> >> >> Has someone out there done a Scirocco MWI
> install
> >> and did they earth the
> >> >> battery bank negative ??
> >> >>
> >> >> I understand that if the PV input is connected
> >> then earthing the battery
> >> >> will upset the GFI on the solar.
> >> >>
> >> >> There is a general debate going over here as
> to
> >> whether to earth battery
> >> >> negative or leave the battery bank to "float"
> >> >>
> >> >> Up to now I have earthed negative in every
> >> install.
> >> >>
> >> >> Comments appreciated
> >> >>
> 
> 
> - - - -
> Hosted by Home Power magazine
> 
> To send a message: RE-wrenches at topica.com
> 
> Archive of previous messages:
> http://lists.topica.com/lists/RE-wrenches/read
> 
> List rules & how to change your email address:
> www.mrsharkey.com/wrenches/etiquette.php
> 
> Check out participant bios:
> www.mrsharkey.com/wrenches/
> 
> Moderator: michael.welch at homepower.com
>
> 
> 
> 
> 
> 



       
____________________________________________________________________________________
Need a vacation? Get great deals
to amazing places on Yahoo! Travel.
http://travel.yahoo.com/


- - - -
Hosted by Home Power magazine

To send a message: RE-wrenches at topica.com

Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read

List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php

Check out participant bios: www.mrsharkey.com/wrenches/

Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at re-wrenches.org

EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com

For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------



More information about the RE-Wrenches mailing list