Switching Array leads[RE-wrenches]
Drake Chamberlin
Drake.Chamberlin at redwoodalliance.org
Sat Jul 28 17:02:12 EDT 2007
<x-flowed>
The ungrounded conductors must be switched. In some systems ( I
think under 50 volts) it is still permissible to not have a grounded
circuit conductor, but to switch both. I believe it is code to
break the grounded conductor with a switch, so long as the ungrounded
conductor breaks at the same time.
Drake
At 06:39 AM 7/28/2007, you wrote:
>As I recall, the older code required both the positive and negative
>leads of an array to be switched at the array dis-connect. I think
>at the time there was no DC ground fault required and most of these
>were low voltage arrays. More recently, I believe the code indicates
>only the "un-grounded" lead to be switched, which would imply just
>the positive lead. Since we now have ground fault circuits I think
>this may also be related to the ground fault working properly since
>it needs to "see" the potential between the grounding conductor and
>the negative before it is grounded.
>
>However, in the recent issue of HomePower there is a system showing
>both the positive and negative leads being switched at the array
>dis-connect. Am I wrong and this is not code, ground fault, or high
>voltage related issue and it is up to the installer? Since all
>dis-connects are either 2 or 3 pole, it is not a cost issue, so
>under what (if any) circumstances would you switch only the positive
>and allow the negative and array frame grounding conductor to pass
>through the dis-connect.
>
>Thanks,
>
>Jeff Yago
>
>_____________________________________________________________
>Netscape. Just the Net You Need.
>
>
>- - - -
>Hosted by Home Power magazine
>
>To send a message: RE-wrenches at topica.com
>
>Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
>
>List rules & how to change your email address:
>www.mrsharkey.com/wrenches/etiquette.php
>
>Check out participant bios: www.mrsharkey.com/wrenches/
>
>Moderator: michael.welch at homepower.com
>
>
>
>
>--
>No virus found in this incoming message.
>Checked by AVG Free Edition.
>Version: 7.5.476 / Virus Database: 269.10.22/923 - Release Date:
>7/27/2007 6:01 PM
- - - -
Hosted by Home Power magazine
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael_welch at sbcglobal.net
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: re-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
</x-flowed>
More information about the RE-Wrenches
mailing list