Galvanic Corrosion [RE-wrenches]

Jim Easton jeaston at ucsd.edu
Thu Jul 19 11:23:57 EDT 2007


<x-flowed>

Galvanic (Electrolytic) corrosion caused by DC current flow is different 
from corrosion caused by soil composition.

Galvanic corrosion such as that caused by a DC ground loop will remove metal 
from the side being corroded in virtually exact proportion to the current 
flowing and the time it flows.

Using copper electrodes can reduce the corrosion since copper has a higher 
electrochemical potential than hydrogen, and the current will preferentially 
decompose water rather than corrode the copper. However, any less refractory 
metal (i.e. iron, steel, zinc, etc.) exposed to the potential will be 
preferentially corroded leading sometimes to rapid failure. This typically 
applies to steel bolts, nuts, washers, and cores of copper clad ground rods 
exposed through abrasion.

Jim Easton, PE
 (E 11974)
4364 Bonita Road, No. 166
Bonita, CA 91902-1421
Tel: 858-527-0240
Fax: 619-470-8616

----- Original Message ----- 
From: "Bill Brooks" <bill at brooksolar.com>
To: <RE-wrenches at topica.com>
Sent: Wednesday, July 18, 2007 10:28 PM
Subject: RE: Inverter location, ground loops, ... [RE-wrenches]


>
> Kent and Jim,
>
> I'm intrigued but not convinced. Does anyone have any evidence out there 
> of
> galvanic corrosion in such a situation? I think there is plenty of 
> evidence
> of corrosive soils, but galvanic corrosion between two rods at 1 Volt
> potential difference being far apart is difficult to believe--guess I need 
> a
> Myth-Busters episode to help me out. I understand Ohm's law, just 
> wondering
> how much resistance and how long it would take to create damage. I'll 
> grant
> a problem with salty wet ground on the beach.
>
> As far as grounding in two places, we are treating the array as a separate
> structure and a separate service at that structure. It may not be the best
> way to do it anyway. The 2008 NEC is likely to allow a frame ground at the
> array without requiring bonding of the electrode to the main building
> grounding system for lightning protection. It is not expressly allowed in
> the code currently. Now we are required to tie the two grounding systems
> together with a grounding electrode conductor.
>
> Bill.
>
> Bill Brooks, PE
> Brooks Engineering
>
>> -----Original Message-----
>> From: Kent Osterberg [mailto:kent at coveoregon.com]
>> Sent: Wednesday, July 18, 2007 5:24 PM
>> To: Wrenches
>> Subject: RE: Inverter location, ground loops, ... [RE-wrenches]
>>
>>
>> Bill,
>>
>> The current that flows through the earth when the ac neutral is grounded
>> at two locations is an ac current, not dc.  As such it contributes
>> little if any to galvanic corrosion.  Grounding a dc current carrying
>> wire in two locations will cause a dc current in the earth which will,
>> if only slowly, cause galvanic corrosion.  Lets assume the grounding
>> resistance is 50-ohms at each end and there is a voltage drop of one
>> volt in the current carrying conductor, that's a 10 mA current.  I don't
>> know how long it'll take, but eventually it'll take all the copper or
>> galvanizing off of a ground rod.
>>
>> Increasing the distance between the two grounds does not help. The
>> incremental resistance is an r-squared function and quickly approaches
>> zero.  If you look at the data for a fall-of-potential test, nearly all
>> of the resistance is near the ground rod.  The fall-of-potential test,
>> is determining the resistance of a ground to a point that is
>> hypothetically infinitely far away.  The resistance between any two
>> grounds is less than the sum of the individual resistance values, but
>> it's only significantly less when the two grounds are close together.
>>
>> In regards to grounding dc systems, take a look at NEC 250.164.  It
>> makes it clear that a dc system is to be grounded at only "one"
>> location, even if that location is off premises (remote).  Given that
>> only one dc ground is allowed and that the earth shall not be used as a
>> grounding conductor, there is no way to install a remote PV array
>> without a ground wire being run with the conductors.  No matter how far
>> away it is.  And the farther away it is the more important it is to have
>> surge arrestors at both ends.
>>
>> Kent Osterberg, PE
>> Blue Mountain Energy, LLC
>
>
> - - - -
> Hosted by Home Power magazine
>
> To send a message: RE-wrenches at topica.com
>
> Archive of previous messages: 
> http://lists.topica.com/lists/RE-wrenches/read
>
> List rules & how to change your email address: 
> www.mrsharkey.com/wrenches/etiquette.php
>
> Check out participant bios: www.mrsharkey.com/wrenches/
>
> Moderator: michael.welch at homepower.com
>
>
>
> 


- - - -
Hosted by Home Power magazine

To send a message: RE-wrenches at topica.com

Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read

List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php

Check out participant bios: www.mrsharkey.com/wrenches/

Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael_welch at sbcglobal.net

EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com

For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------


</x-flowed>


More information about the RE-Wrenches mailing list