Bill,
Did you mean to say tripping of "because of high voltage at the inverter
terminals," amigo? Seems to me, at least in these here parts, that a 3
percent voltage drop usually means a lower voltage at the terminals, no?
marco
Having seen numerous inverters tripping off line because of high voltage at
the inverter terminals (due to 3% voltage drop on the ac side), this is a
critical operational issue.
Bill.