Kurt,
The output (A/C) of the inverter can be installed in any approved raceway or 
cable assembly.  PVC (sch 80 if exposed) is an approved method.  The metal 
raceway rule only applies to the unfused D/C output of the array.  If you 
are installing a high voltage system, the voltage drop is similar for A/C or 
D/C. Either way would work.
Mike Bernhard


----- Original Message ----- 
From: "Kurt Nelson" <sunwise at cheqnet.net>
To: <RE-wrenches at topica.com>
Sent: Monday, July 09, 2007 2:59 PM
Subject: Inverter location [RE-wrenches]


>
> Greetings all,
>
> I'm doing a 3,200 watt pole mounted system with an SMA inverter.  It
> looks like I can have the inverter out at the array, or indoors by the
> service entrance.
>
> Does the code require metallic conduit inside the building in either
> case, or if it is the ac output of the inverter (mounted out at the
> array), can it be in PVC and/or within wall cavities, etc.?
>
> Which location do most folks prefer.
>
> Thanks in advance,
>
> Kurt
>
> ----------------------------------------------------------------
>
> Kurt Nelson
> PO Box 309
> Cornucopia, WI 54827
> 715-742-3406
> sunwise at cheqnet.net
>
>
> - - - -
> Hosted by Home Power magazine
>
> To send a message: RE-wrenches at topica.com
>
> Archive of previous messages: 
> http://lists.topica.com/lists/RE-wrenches/read
>
> List rules & how to change your email address: 
> www.mrsharkey.com/wrenches/etiquette.php
>
> Check out participant bios: www.mrsharkey.com/wrenches/
>
> Moderator: michael.welch at homepower.com
>
>
>
>
> 


- - - -
Hosted by Home Power magazine

To send a message: RE-wrenches at topica.com

Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read

List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php

Check out participant bios: www.mrsharkey.com/wrenches/

Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael_welch at sbcglobal.net

EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com

For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------


</x-flowed>


More information about the RE-Wrenches mailing list