Tripping breaker [RE-wrenches]
Drake Chamberlin
Drake.Chamberlin at redwoodalliance.org
Thu May 3 12:26:21 EDT 2007
I had a similar problem on an old Sun Tie, that
drove me nuts. The breakers on the unit wouldn't blow when the inverter was
switched on, although the breakers in the main box would, even though they were
rated at 20 amps compared to 15 amps in the unit (as I recall).
I turned out that the capacitors charging were the culprit. The reason
the breakers in the box would blow, even though of higher rating, was that the
particular brand of breaker just happened to blow more quickly! Tech
support theorized this. When 30 amp breakers were used in the main box
with #10 wire to the inverter, all worked fine.
Drake
[Non-text portions of this message have been removed]
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: re-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------