Breaker space in PS-2DC [RE-wrenches]
Geoff Greenfield
Geoff at Third-Sun.Com
Tue Apr 24 15:48:54 EDT 2007
I have a customer with a PS-2DC with 2 inverters and 2 MX-60s... He would
like to expand his array (adding a 3rd MX-60). The problem is we have only
3 breaker spaces left and I figure I need 3 for a second GFI and a fourth
for the DC disco to the MX-60.
The mx-60 could be current limited to 43 amps - what would you all say to
using the gfi on both sides (prob no good as I think the gfi is not a
current limiting device). Maybe I could add a DC fuse inside to handle that
and just use the gfi as disconnect means.
Other work around would be a kluged add on box to hold a DC breaker (or
GFI). Not clean, but do-able.
This is rural and not inspected but our policy is to work safely and to the
NEC (or to it's intent when we are the design review).
Any suggestions would be appreciated!
For a brighter energy future,
Geoff Greenfield
President
Third Sun Solar & Wind Power Ltd.
340 West State street, Unit 25
Athens, Ohio 45701
(740) 597-3111 fax: (740)597-1548
www.third-sun.com
Clean Energy - Expertly Installed
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
More information about the RE-Wrenches
mailing list