sharing conduit [RE-wrenches]
Nicholas Ponzio
wrench at vtsolar.com
Wed Apr 18 10:42:54 EDT 2007
Is there a way to legally run AC inverter output through a conduit (2" PVC)
that already has co-axial TV cable in it?
My reading of the code (see below) suggests that we need a "permanent
barrier or listed divider." What constitutes a divider?
Thanks in advance for any suggestions or insights.
* NEC Reference:
800.113.A.1.5.c Communications conductors shall not be placed in any
raceway, compartment, outlet box, junction box, or similar fitting with
conductors of electric light, power, Class 1, non-power-limited fire alarm,
or medium power network-powered broadband communications circuits.
Exception No. 1: Where all of the conductors of electric light, power, Class
1, non-power-limited fire alarm, and medium power network-powered broadband
communications circuits are separated from all of the conductors of
communications circuits by a permanent barrier or listed divider.
- - - -