Grounding on granite island [RE-wrenches]

Ray Walters walters at taosnet.com
Sat Apr 7 13:52:27 EDT 2007


<x-flowed>


We did an installation on a rocky mountain top in West Texas several  
years ago. Same thing:  solid rock 6" below the surface. This system  
featured a 50 ft tall wind generator as well. We dutifully tied all  
the grounds together, ran copper outside of the conduit to enhance  
the conductivity to ground, put in polyphasor lightning protection, etc.
A lightning strike apparently to the wind generator sent a surge  
through the grounding system that took out 2 SW4024s, the charge  
controller, the Omnimeter, and the Kohler control for the generator.
After that, we ran a 1/2" steel cable  ( that's what they had  
already) and ran it from our existing ground system a 1/2 mile to a  
steel cased well in the valley below. Seems to have done the trick,  
as we haven't had any trouble since. That is a lot of cable, but that  
was a lot of equipment taken out too.

Ray Walters


On Apr 7, 2007, at 5:44 AM, Ken Schaal wrote:

>
> Several years ago we designed and furnished an off grid 2 kw system  
> for an extremely remote research facility in Gabon, Africa. It is  
> located on a huge slab of rock in the middle of the rain  
> forest ,with tall trees all around, on the equator and miles from  
> the nearest dirt road. Most supplies were delivered by helicopter.  
> All the buildings were built on piers on the rock, so a Ufer was  
> not an option. Shallow wet ground was several hundred feet away at  
> the edge of the rock and near a shallow river. So we supplied a  
> large sheet of recycled heavy gauge copper roofing with copper  
> grounding cable soldered to it, and several clamps to attach a #4  
> copper ground wire from the array and inverters. Surge protectors  
> were of course built in to the Outback power panel . 302's I think,  
> probably should have used the really good one's from Polyphaser, I  
> think. Instructions were to bury this copper plate in as wet a  
> place ,and as deep, as possible. They have quite a few lightning  
> storms. So far they are quite pleased with the system, which powers  
> the office and kitchen, including refrigeration. IE; It hasn't been  
> zapped yet !
>
> My questions to the assembled wisdom of this group are;
> -- was this the best solution and/or could it be improved?
> --During the dry season, should they be sure to keep wet the area  
> where it is buried ?
> --Should a lightning protection system, like those used on houses,  
> be considered? Or is the marginal grounding point the main issue?
> --What is the best way to test the effectiveness of the existing  
> ground system, including the path from PV panel to mounting system  
> [ alum. rack on wooden support     structure] to ground wire across  
> rock?
>        This wire by the way, was supposed to have been encased in  
> latex modified cement mortar to fasten it to the rock so the people  
> and elephants wondering thru         camp wouldn't dislodge it !
> --What else should be considered?
>
> Everything has to be shipped by container from NY. We have some  
> smaller systems leaving in several weeks, and if improvements are  
> to be made, this would be the time.
>
> Thank you in advance for your thoughts, and time.
>
> Ken Schaal
> CommonWealthSolar,LLC
>
>
>
> ----- Original Message ----- From: "Phil Undercuffler"  
> <p.undercuffler at conergy.us>
> To: <RE-wrenches at topica.com>
> Sent: Friday, April 06, 2007 10:59 PM
> Subject: RE: Grounding on granite island [RE-wrenches]
>
>
>>
>> Are they pouring concrete footers?
>>
>> Establish a Ufer ground by tying to the rebar in the foundation.  
>> Here in
>> the dry Southwest, it's the preferred grounding method in the area --
>> fast, easy, effective and very nearly free.
>>
>> Have the concrete sub bend up a piece of the footing rebar, and leave
>> 9-10" exposed out of the slab in the area of the power system.   
>> Connect
>> to it with a two piece grounding "saddle" clamp, which makes a  
>> bronze to
>> steel connection, and keeps the copper conductor isolated from the
>> steel.
>>
>> Of course, if they aren't pouring a concrete foundation this wouldn't
>> help.
>>
>>
>> ------------------------------------------------------------------
>>
>> Phil Undercuffler
>> Technical Services Manager
>> Conergy, Inc.
>> 1730 Camino Carlos Rey Suite 103
>> Santa Fe NM 87507 USA
>> Office | 505.473.3800 x4841
>> Fax | 505.473.3830
>> www.conergy.us
>>
>> ------------------------------------------------------------------
>>
>> -----Original Message-----
>> From: Michael Welch [mailto:michael.welch at homepower.com]
>> Sent: Friday, April 06, 2007 10:57 AM
>> To: RE-wrenches at topica.com
>> Subject: Grounding on granite island [RE-wrenches]
>>
>>
>> Hi gang I an email awhile back about a grounding question, and a
>> follow-up phone call today.
>>
>> This fellow is building a PV/wind/generator system for small  
>> cottages on
>> a solid granite rock out on Lake Huron. His earth grounding plan  
>> is to
>> haul a big steel plate out onto the ice (will need to do this pretty
>> soon) and let it sink to the lake floor as a way of grounding the
>> system.
>>
>> Or he may be able to submerge a plate in his graywater pool.
>>
>> There is no more than 6 inches of earth above the granite on the  
>> island.
>> He does not have access to the kind of equipment needed to drill deep
>> holes in the granite, but he can drill 6 or so inches deep.
>>
>> His RE dealer has been no help because of the unusual nature of the
>> problem, and he has not been able to get help from local electrical
>> engineers and electricians for the same reason.
>>
>> He wants to know if he is doing this correctly, and what size  
>> plates to
>> use, how many, and anything else you can think of.
>>
>> You can either respond here if you think it will be of interest to  
>> the
>> list, or if you need more info and want to carry out an email
>> conversation with him, let me know off list and I will get you his  
>> email
>> address.
>>
>> Thanks in advance for your help.
>>
>>
>> ------------------------
>> Michael Welch
>> Sr. Editor
>>     Home Power magazine
>>     www.homepower.com
>>
>>
>> - - - -
>> To send a message: RE-wrenches at topica.com
>>
>> Archive of previous messages:
>> http://lists.topica.com/lists/RE-wrenches/read
>>
>> List rules & how to change your email address:
>> www.mrsharkey.com/wrenches/etiquette.php
>>
>> Check out participant bios: www.mrsharkey.com/wrenches/
>>
>> Hosted by Home Power magazine
>>
>> Moderator: michael.welch at homepower.com
>>
>>
>> - - - -
>> To send a message: RE-wrenches at topica.com
>>
>> Archive of previous messages: http://lists.topica.com/lists/RE- 
>> wrenches/read
>>
>> List rules & how to change your email address: www.mrsharkey.com/ 
>> wrenches/etiquette.php
>>
>> Check out participant bios: www.mrsharkey.com/wrenches/
>>
>> Hosted by Home Power magazine
>>
>> Moderator: michael.welch at homepower.com
>>
>>
>>
>
>
> - - - -
> To send a message: RE-wrenches at topica.com
>
> Archive of previous messages: http://lists.topica.com/lists/RE- 
> wrenches/read
>
> List rules & how to change your email address: www.mrsharkey.com/ 
> wrenches/etiquette.php
>
> Check out participant bios: www.mrsharkey.com/wrenches/
>
> Hosted by Home Power magazine
>
> Moderator: michael.welch at homepower.com
>
>
>

R. Walters
Solarray.com
NABCEP # 04170442	




--
[Non-text portions of this message have been removed]


- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read

List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php

Check out participant bios: www.mrsharkey.com/wrenches/

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com

EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com

For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------


</x-flowed>


More information about the RE-Wrenches mailing list