Are they pouring concrete footers?  

Establish a Ufer ground by tying to the rebar in the foundation. Here in
the dry Southwest, it's the preferred grounding method in the area --
fast, easy, effective and very nearly free.

Have the concrete sub bend up a piece of the footing rebar, and leave
9-10" exposed out of the slab in the area of the power system.  Connect
to it with a two piece grounding "saddle" clamp, which makes a bronze to
steel connection, and keeps the copper conductor isolated from the
steel.  

Of course, if they aren't pouring a concrete foundation this wouldn't
help.  

 
------------------------------------------------------------------
 
Phil Undercuffler
Technical Services Manager
Conergy, Inc. 
1730 Camino Carlos Rey Suite 103
Santa Fe NM 87507 USA
Office | 505.473.3800 x4841
Fax | 505.473.3830
www.conergy.us 
 
------------------------------------------------------------------

-----Original Message-----
From: Michael Welch [mailto:michael.welch at homepower.com] 
Sent: Friday, April 06, 2007 10:57 AM
To: RE-wrenches at topica.com
Subject: Grounding on granite island [RE-wrenches]


Hi gang I an email awhile back about a grounding question, and a
follow-up phone call today. 

This fellow is building a PV/wind/generator system for small cottages on
a solid granite rock out on Lake Huron. His earth grounding plan is to
haul a big steel plate out onto the ice (will need to do this pretty
soon) and let it sink to the lake floor as a way of grounding the
system. 

Or he may be able to submerge a plate in his graywater pool.

There is no more than 6 inches of earth above the granite on the island.
He does not have access to the kind of equipment needed to drill deep
holes in the granite, but he can drill 6 or so inches deep.

His RE dealer has been no help because of the unusual nature of the
problem, and he has not been able to get help from local electrical
engineers and electricians for the same reason.

He wants to know if he is doing this correctly, and what size plates to
use, how many, and anything else you can think of. 

You can either respond here if you think it will be of interest to the
list, or if you need more info and want to carry out an email
conversation with him, let me know off list and I will get you his email
address. 

Thanks in advance for your help.

  
------------------------
Michael Welch
Sr. Editor
     Home Power magazine
     www.homepower.com


- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages:
http://lists.topica.com/lists/RE-wrenches/read

List rules & how to change your email address:
www.mrsharkey.com/wrenches/etiquette.php

Check out participant bios: www.mrsharkey.com/wrenches/

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com


- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read

List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php

Check out participant bios: www.mrsharkey.com/wrenches/

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com

EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com

For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------





More information about the RE-Wrenches mailing list