Advise sought for large off grid PV system; 480 volt 3-phase [RE-wrenches]
larry crutcher
larry at starlightsolar.com
Tue Mar 27 16:59:06 EDT 2007
RE-Wrenches,
I am designing an off grid PV system and am looking for input and
recommendations from experienced installers. Although I have years of
building battery based systems, this is a big one. The customer has been
running 60kW diesel generators 24/7 for about 2 decades. They want a PV
system with batteries that will allow the generators to be shut down
during the winter and low load periods. Summer loads can be above
500kWhs per day but winter drops to less than 100kWhs which I can do
with PV's.
Power details: The site has 480 volt, 3-phase Y distribution and 6
transformers. There are only two 480 volt distribution circuits leaving
the generator building. I have failed to locate power equipment that
will produce 480 volt 3 phase for off grid use. Telecom equipment does
not look suitable. I have found inverters to produce 60 kW @ 208 volt 3
phase (Exeltech) and a 75 kva step up transformer for 480Y. I don’t like
the transformer idea. The generator must be available at any time to
take over loads. I am thinking of transfer switching @ 480 volts. I
really would like automation for generators, battery charging, and
transfer switches.
One generator is scheduled for rebuild and it will have auto-start added
to it. The site has room for several large ground mount arrays of PV.
Wind power does not look viable, < 5 m/s @ 30 meters. I am in a desert
location that has very high ambient temperatures above 115°. A building
for the batteries and inverters will be climate controlled to 80° F.
So, how would you propose a solution for this type of site? Do you know
where I can get 480 3-phase inverters?
Next post I'll ask about batteries, BIG batteries. No, even bigger!
Larry Crutcher
Starlight Solar
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
More information about the RE-Wrenches
mailing list