I have running a set of Surrettes (Rolls) for about eight months.  
They do come up to voltage pretty quickly, even brand new, when I use  
the generator, but they do go ahead and accept a pretty hefty rate of  
current (>70 amps) for a number of hours before they start to taper  
down. I do expect to have to apply the C10 rate on a reqular basis as  
part of maintaining these batteries.

If these batteries are near as good and long lasting as my last set  
I'll be pleased. My last set were Global Yuasa tubular plate 2 Vdc  
cells. I got them from Davidson Battery Service in Vancouver B. C,  
and they lasted a full 14 years in my application - nasty care, heavy  
loads etc. They are now "resting" in light duty service in an  
application with less load demand. These batteries too wanted a C10  
charge rate for initial charging.

I'd not shy away from Surrette (Rolls) but I would be sure to have an  
adequately sized charging system. A basic rule of thumb for me is too  
much lead and too little silicone = the need for a big generator for  
occasional use.

Cheers,

Ezra Auerbach

DragonSun Consulting
Lasqueti Island, B.C. V0R 2J0

ezra at lincsat.com
250 333 8650




On 13-Mar-07, at 5:21 PM, Drake Chamberlin wrote:

>
> Do the Surretts still require a C/5 charge, once per week, as  
> stated on the list previously, to keep the warranty valid?  If so,  
> they are worthless for most PV applications, IMHO.
>
> Drake
>
> At 03:49 PM 3/13/2007, you wrote:
>
>> Ray,
>>
>> I've been told at various times that the characteristics you're  
>> describing are the sign of a highly sulfated battery.  That is,  
>> the sulfation causes a higher source impedance such as you're  
>> seeing.  Did any of the sets see long term intervals of time where  
>> they weren't able to reach full charge?  Are you considering using  
>> one of the anti-sulfation pulsing tools on any of the battery  
>> banks?  Maybe they're more prone to sulfation degradation than  
>> other types.
>>
>> I'm curious to hear all that I can on the Surrettes.  We're  
>> looking at switching to them in a major way this season due to  
>> both pricing and sourcing issues with Trojan in our region.  But  
>> the kind of issues that you and Alan have brought up aren't making  
>> this the slam dunk I had hoped...
>>
>> John Raynes
>> RE Solar
>> Torrey, UT
>>
>>
>>
>> At 04:21 PM 3/12/2007 -0600, you wrote:
>>
>>> Good News on the HUP, as the Rolls 5000s we installed about 1 to 2
>>> years ago are having very disquieting performance. 3 different  
>>> sets I
>>> have tested all behave as if they are close to "death". They quickly
>>> run to below nominal voltage when loaded, and then when charged at a
>>> c10 to c20 rate, they go to equalize voltages within 5 minutes. If I
>>> had just been called out on an old system and saw numbers like that,
>>> I would be shaking my head and recommending a new set of
>>> batteries.... only I just sold these people new batteries, and  
>>> talked
>>> them into the "better", more expensive Rolls. The Rolls were easier
>>> to install than the HUPs, but the HUPS, Bulldogs, Exide Industrial,
>>> etc. that I have installed have been very stable, with no problems
>>> what so ever. Some have been in for almost 10 years.
>>> Rolls seem to be a completely different battery, they don't like to
>>> be discharged hard at all. I'm cringing on providing the extended
>>> warranty I promised too. At least they're easier to move.....I  
>>> hope I
>>> don't have to.
>>>
>>> Ray
>>
>>
>> - - - -
>> To send a message: RE-wrenches at topica.com
>>
>> Archive of previous messages: http://lists.topica.com/lists/RE- 
>> wrenches/read
>>
>> List rules & how to change your email address: www.mrsharkey.com/ 
>> wrenches/etiquette.php
>>
>> Check out participant bios: www.mrsharkey.com/wrenches/
>>
>> Hosted by Home Power magazine
>>
>> Moderator: michael.welch at homepower.com
>>
>>
>>
>>
>> --
>> No virus found in this incoming message.
>> Checked by AVG Free Edition.
>> Version: 7.5.446 / Virus Database: 268.18.11/721 - Release Date:  
>> 3/13/2007 4:51 PM
>
>
> - - - -
> To send a message: RE-wrenches at topica.com
>
> Archive of previous messages: http://lists.topica.com/lists/RE- 
> wrenches/read
>
> List rules & how to change your email address: www.mrsharkey.com/ 
> wrenches/etiquette.php
>
> Check out participant bios: www.mrsharkey.com/wrenches/
>
> Hosted by Home Power magazine
>
> Moderator: michael.welch at homepower.com
>
>






--
[Non-text portions of this message have been removed]


- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read

List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php

Check out participant bios: www.mrsharkey.com/wrenches/

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com

EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com

For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------


</x-flowed>


More information about the RE-Wrenches mailing list