AC Connection at Fused Disconnect [RE-wrenches]

Mark Frye markf at berkeleysolar.com
Mon Feb 5 21:13:18 EST 2007


Allen,

Thanks for sending me the article the other day. I read it carefully.

As I mentioned, John does not specifically address the issue of a LOAD side
connection with a fused disconnect.

I am in the process of communicating with him about this to clarify his
understanding of the issue.

There seems to be some confusion between doing a LOAD side tap (690.64(B))
and doing a SUPPLY side tap where the OCP has to be within the service
equipment itself or adjacent to the service equipment (690.64(A) referencing
230.82(6) leading to 230.91).

My permit went in for review today and I am waiting to hear what the plan
checker says.

MPF

-----Original Message-----
From: Allan Sindelar [mailto:allan at positiveenergysolar.com]
Sent: Sunday, February 04, 2007 9:00 AM
To: RE-wrenches at topica.com
Subject: Re: AC Connection at Fused Disconnect [RE-wrenches]



Mark,
It seems to me that this is the perfect situation for you to use John Wiles'
work. He has written that it is acceptable. He has published this as a lead
article in the September-October IAEI (International Association of
Electrical Inspectors, I think) journal. The article can be readily
downloaded as a .pdf file. He heads the Code revision panel for PV. If you
can't convince your local AHJ that it's legal with all this ammunition, you
must have forgotten the doughnuts.

Just to make it overkill, I'm sending you the .pdf article offlist. Anyone
else, it can be found via links at http://www.NMSU.Edu/~tdi.

Allan


- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read

List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php

Check out participant bios: www.mrsharkey.com/wrenches/

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com

EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com

For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------






More information about the RE-Wrenches mailing list