Hey Todd,

I don't know the circumstances with this well, but I find well drillers
here in WI consistently undersize the current carrying conductors on
these pumps.  

What's the distance from the pump placement in the well all the way to
the breaker box and what size wire did they install?  You can usually go
to the pump manufacturer's web page and view a PDF of cable sizing for
their pumps.

And if you're using a transformer, and if there's any real distance from
the inverter to the transformer, remember this wire is carrying twice
the current on the 120vac input as the 240vac output.  

Kurt

----------------------------------------------------------------

Kurt Nelson
PO Box 309
Cornucopia, WI 54827
715-742-3406
sunwise at cheqnet.net


-----Original Message-----
From: Todd Cory, Mt. Shasta Energy Services
[mailto:toddcory at finestplanet.com] 
Sent: Friday, January 26, 2007 12:54 PM
To: Wrenches
Subject: starting a 1 HP well pump with a VFX3648 [RE-wrenches]


Wrenches,

I have an off grid customer with a Outback VFX3648. They have a 3 wire, 
1 HP well pump that is on the hairy edge of operating, occasionally 
overloading the inverter on startup. I have thought about the possible 
easy solutions to this problem. One is a suggestion I have heard from 
wrenches about changing the starting capacitor on the pump's starter. 
Does this work and if so does anyone know which way to go (larger mfd or

smaller)? Also is there an after market "soft start" unit that could be 
put on this pump? Any other options / suggestions would be appreciated.

Thanks,

Todd


- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages:
http://lists.topica.com/lists/RE-wrenches/read

List rules & how to change your email address:
www.mrsharkey.com/wrenches/etiquette.php

Check out participant bios: www.mrsharkey.com/wrenches/

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com


- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read

List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php

Check out participant bios: www.mrsharkey.com/wrenches/

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com

EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com

For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------









More information about the RE-Wrenches mailing list