I wanted to see if there is a consensus on the subject of sizing long 
residential feeders.  I have some off-grid jobs coming up with feeders 
anywhere from 350 to 530 conduit feet and I need to specify feeder 
sizes.  Here's the philosophy I have been using, I'd be curious if anyone 
disagrees:

NEC 215.2 A (4) specifies feeders to not exceed 3% VD.  I agree this is 
appropriate for considering VD for the maximum draw I might 
expect.  Furthermore, I imagine that peak current draw will occur 
infrequently (or these customers are going to exceed the capability of 
their systems on a regular basis).

I base my calculations on a maximum draw of 50 amps for the larger off-grid 
residences I am now designing for.  If the VD approaches 3% at 50 amps, it 
is not much above 1% for 30 amp draws.  I figure staying in this range is safe.

Comments from this group are always greatly appreciated.

William Miller




__________________________________________________________________
William Miller
Miller Power and Communications
Voice :805-438-5600     Fax: 805-438-4607
email: wrmiller at mpandc.com
http://mpandc.com
License No. C-10-773985
_____________________________________________________________
Check out our latest project at 
http://mpandc.com/case_studies/pv_school/pv_school.html 


- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read

List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php

Check out participant bios: www.mrsharkey.com/wrenches/

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com

EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com

For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------



</x-flowed>


More information about the RE-Wrenches mailing list