Outback with Sunnyboy [RE-wrenches]
David Katz
david at aeesolar.com
Sun Dec 3 15:14:55 EST 2006
<x-flowed>
Drake,
I have been doing the same thing for a couple of years. The only thing
to have to add is a way to turn off the output of the Sunnyboy when the
batteries are fully charged and the grid is down.
This is necessary when the grid is down because the inverters will
charge batteries with the excess power generated through the array
through the Sunnyboy. Since you are feeding ac into the output of the
Outback inverters, there is not charging control. I used the auxiliary
12 volt output to power a relay between the Sunny boy and the sub panel
so that when the batteries reach a full charge voltage, the relay opens
and the Sunnyboy thinks the grid is down and turns off. The relay will
close when the batteries drop in voltage and the Sunnyboy will think the
grid is back on and its will send power to the sub panel again. Voltage
setting will depend on the type of battery you are using. This system
works great because you get the efficiency of the Sunnyboy plus backup
power.
David
David Katz
AEE Solar, Inc.
formerly Alternative Energy Engineering
1155 Redway Drive - Box 339
Redway, CA 95560 USA
Phone 707-825-1200
Fax 707-825-1202
email david at aeesolar.com
www.aeesolar.com
Drake Chamberlin wrote:
>
>
>
>
> Hi Wrenches,
>
>
>
> We are planning to feed the grid with a pair of Stacked Outbacks and a Sunnyboy, which we would like to feed into the same subpanel. The Outbacks will supply battery backup. The sub panel will feed the grid ahead of the service disconnect in the main panel.
>
>
>
> Does this create any islanding potential, or any other problems that anyone knows about?
>
>
>
> Thanks,
>
>
>
> Drake
>
>
>
>
>
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
</x-flowed>
More information about the RE-Wrenches
mailing list