Sayo HIP Modules with MX60 [RE-wrenches]

Nicholas Ponzio wrench at vtsolar.com
Fri Nov 3 08:29:10 EST 2006


I just came across a similar situation (with HIP-200BA3 in a 48V battery
system) and in digging around on the Outback forum I discovered mention of
the Sanyo HIP-210NHE1. This module has a Voc of 50.9 so it can be used in
series pairs of 2 each without exceeding the MX60 limit. The question is can
we get them in the States? 






-----Original Message-----
From: Ryan Mayfield [mailto:ryan_mayfield at earthlink.net] 
Sent: Thursday, November 02, 2006 11:34 AM
To: RE-wrenches at topica.com
Subject: Re: Sayo HIP Modules with MX60 [RE-wrenches]


Jeremy,

To determine the adjusted Voc use the formula:
 
Vadj = Voc + ((Tcell - Tstc) * temp coefficient)

Note the temperatures are in degrees C with Tstc = 25C. 

Also, you should use coldest temperature, not coldest daytime ambient
temperature. Your modules will go to Voc early in the morning before the sun
strikes the modules and produce any current. It is generally recommended to
use record low temperature for that calculation, that way you should never
exceed voltage limits. OutBack has some protection to compensate for over
voltage conditions but a good design practice would be to avoid that
situation altogether, especially if you can find yourself exceeding 150Voc
on a regular basis.

That said I think you are in a tough spot. If you put two modules in series
you will exceed the 150Voc limit but if you don't the voltage loss due to
heat in the summer will drop you below your battery charging voltage. In
that case, I think the MX60 would hold your array at the necessary voltage
to charge your batteries but it will have to come at the cost of the
current.

Seems to me like these aren't the best panels for your situation.

Ryan



-----Original Message-----
>From: Darren Emmons <darren at solarhacker.com>
>Sent: Nov 1, 2006 9:48 PM
>To: RE-wrenches at topica.com
>Subject: Re: Sayo HIP Modules with MX60 [RE-wrenches]
>
>
>Jeremy,
>
>See Outback Forum for postings on MX60 and Sanyo modules.
>
>http://www.outbackpower.com/forum/viewtopic.php?t=1481
>
>
>Darren
>Solar Hacker Software
>North Bend, WA
>
>
>Jeremy Rodriguez wrote:
>> Wrenches, 
>> I have a customer with HIP 195's to connect to an MX60. Battery voltage 
>> is 48. The VOC nameplate rating is 68.1 each module. I'm not sure how to 
>> compute the Temp Coefficient of -0.170 (V/degC). The coldest ambient 
>> daytime temp could be 10F here in Colorado. Any help or advise would be 
>> appreciated.
>>
>> Jeremy
>> All Solar
>> Penrose, CO
>>
>>
>> - - - -
>> To send a message: RE-wrenches at topica.com
>>
>> Archive of previous messages:
http://lists.topica.com/lists/RE-wrenches/read
>>
>> List rules & how to change your email address:
www.mrsharkey.com/wrenches/etiquette.php
>>
>> Check out participant bios: www.mrsharkey.com/wrenches/
>>
>> Hosted by Home Power magazine
>>
>> Moderator: michael.welch at homepower.com
>>
>>
>>   
>
>
>- - - -
>To send a message: RE-wrenches at topica.com
>
>Archive of previous messages:
http://lists.topica.com/lists/RE-wrenches/read
>
>List rules & how to change your email address:
www.mrsharkey.com/wrenches/etiquette.php
>
>Check out participant bios: www.mrsharkey.com/wrenches/
>
>Hosted by Home Power magazine
>
>Moderator: michael.welch at homepower.com
>
>


- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read

List rules & how to change your email address:
www.mrsharkey.com/wrenches/etiquette.php

Check out participant bios: www.mrsharkey.com/wrenches/

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com


- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read

List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php

Check out participant bios: www.mrsharkey.com/wrenches/

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com

EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com

For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------







More information about the RE-Wrenches mailing list