Branch circuits in Subpanels [RE-wrenches]

Jeff Clearwater clrwater at earthlink.net
Tue Oct 31 07:02:52 EST 2006


<x-flowed>

Hi Dan,

Reason Prevails!

Thanks,

Jeff C.
Village Power Design




>Steve et. al.
>
>With all due respect, 312.8 says "Enclosures for switches or 
>overcurrent devices
>shall not be used as junction boxes, auxiliary gutters, or raceways for
>conductors feeding through or tapping off to other switches or overcurrent
>devices, unless adequate space for this purpose is provided. The conductors
>shall not fill the wiring space at any cross section to more than 40 
>percent of
>the cross-sectional area of the space, and the conductors, splices, and taps
>shall not fill the wiring space at any cross section to more than 75 
>percent of
>the cross-sectional area of that space."
>
>Splices are specifically allowed under the conditions specified, wire nuts
>included.
>
>Dan Rice
>Abundant Sun, LLC.
>
>Quoting Steve Lyons <sinepv at hotmail.com>:
>
>>
>>  Hi Geoff!
>>
>>  Please see 2002 NEC Art. 312.8 " Enclosures for Switches or Overcurrent
>>  Devices".
>>  The first sentence says it all " Enclosures for switches or overcurrent
>>  devices SHALL NOT be used as junction boxes".
>>
>>  During my 30+ years as a journeyman, I have seen breaker panels with wire
>>  nuts and taped split bolt splices, it is not goog practice or acceptable.
>>
>>  We all should know the NEC requirements as well as we do the solar.
>>
>>  Hope this helps.
>>
>>  Stephen Lyons
>>  Sine Electric
>>  C-10 & General Journeyman Electrician
>>  324 Grandview Avenue
>>  Novato, CA 94945
>>
>>  sinepv at hotmail.com
>>
>>  >From: Geoff Greenfield <Geoff at Third-Sun.Com>
>>  >Reply-To: RE-wrenches at topica.com
>>  >To: RE-wrenches at topica.com
>>  >Subject: Re: Branch circuits in Subpanels [RE-wrenches]
>>  >Date: Mon, 30 Oct 2006 15:23:02 -0500
>>  >
>>  >
>>  >Has anyone ever been hassled about having wire nuts in a load center?  A
>>  >local inspector we had a pre-job plan review with told us that the load
>>  >center is not listed as a junction box.  He said we had to pull the romex
>>  >out and splice extensions to the new sub panel.
>>  >
>>  >For a brighter energy future,
>>  >
>>  >Geoff Greenfield
>>  >NABCEP Certified Energy Practitioner
>>  >
>>  >THIRD SUN SOLAR & WIND POWER Ltd.
>>  >340 West State Street
>>  >Athens, OH 45701
>>  >
>>  >www.third-sun.com
>>  >(740) 597-3111
>>  >
>
>
>
>----------------------------------------------------------------
>SCI WebMail http://webmail.scinternet.net/
>
>
>- - - -
>To send a message: RE-wrenches at topica.com
>
>Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
>
>List rules & how to change your email address: 
>www.mrsharkey.com/wrenches/etiquette.php
>
>Check out participant bios: www.mrsharkey.com/wrenches/
>
>Hosted by Home Power magazine
>
>Moderator: michael.welch at homepower.com


-- 
~~~~~~~~~~~~~
Jeff Clearwater
Village Power Design
Sustainable Energy & Water Solutions for Home & Village
http://www.villagepower.com
gosolar at villagepower.com
NABCEP (tm) Certified Solar PV Installer

530-470-9166
877-SOLARVillage
877-765-2784
65 Schoolhouse Rd
Amherst, MA 01002
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~`~


- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read

List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php

Check out participant bios: www.mrsharkey.com/wrenches/

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com

EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com

For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------


</x-flowed>


More information about the RE-Wrenches mailing list