690-64 (B)(2) [RE-wrenches]
Bill Brooks
bill at brooksolar.com
Sun Oct 29 13:58:51 EST 2006
Steve,
If the panel does not already have double lugs, most panels like this can be
fitted with a double lug kit. You still have to have the utility shut down
power, but it can be easier than piercing lugs for a line side tap if the
input conductors are inaccessible.
We continue to fight the fight on the NEC level on this issue so wish us
luck at the meeting in November. I was the one to get the proposal for the
opposite end into the 2008 proposals. They accepted the idea in principle,
but other groups have questioned it. We hope that straight thinking will
prevail over a focus on how many code violations it takes to create a safety
problem with this concept.
Bill.
> -----Original Message-----
> From: Steve Johnson [mailto:stevejohnson at comcast.net]
> Sent: Sunday, October 29, 2006 8:27 AM
> To: RE-wrenches at topica.com
> Subject: RE: 690-64 (B)(2) [RE-wrenches]
>
>
> I haven't taken the cover off the panel yet, but I would expect the bus
> bars to be AFTER the main breaker. On a main lug panel I can see it,
> but this has a main breaker. So if you tap the bus and go to a
> disconnect then the rating of the disconnect has to be added to the main
> and you are right back where you were. By the way I need to tap for 35
> amps, 2 pole.
>
> Checking with the panel engineers for a higher bus rating is a thought.
> Unfortuately it is GE, the most unresponsive of the 4 major
> manufacturers in my experience, but I'll give em a try.
>
> J Wiles mentioned main breakers with double rated lugs, so I can talk to
> them about that as well.
>
> and then there is the old Kup-L-tap, made by Ilsco.
> http://ebusiness.ilsco.com/webapp/wcs/stores/servlet/CategoryDisplay?store
> Id=10001&langId=-1&catalogId=1&categoryId=151
>
>
> I still think this requirement is onerous and hasn't been thought out
> well, but that's not the topic of this post. It seems like if the PV
> was at the opposite end of the bus from the incoming power, with the
> loads in the middle, the bus could never carry 835 amps.
>
> Thanks for the suggestions and ideas.
>
> Steve
>
> Steve Johnson
> LightWave Electric
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
More information about the RE-Wrenches
mailing list