downsizing main breakers [RE-wrenches]
Steve Johnson
stevejohnson at comcast.net
Sun Oct 22 13:43:28 EDT 2006
The easy way to measure the load is put an amprobe around the incoming
service conductors at the panel and turn on everything in the house that
can be turned on, and I mean everything! Then check the other leg.
Neutral should be the difference between the two. If you are 120 amps
or less (80% of 150) you are good to go. You could go above that, 130
or 140 amps with the owners agreement, since a second source of power is
being added. Loads can be added to any panel anywhere thereby
overloading any service, ie, you can overload that 200 amp breaker too -
some future owner could. But I would definitely find out if they have
natural gas or propane and what it runs. The point is to design for
current known and expected conditions. Besides, by downsizing the main
overcurrent protection you are providing more protection not less. The
point is not to downsize beyond potential existing or known planned
future loading.
Secondly taping the service overhead is not as hard as it may seem. The
tap someone mentioned earlier is called a Kupltap. It is insulated and
can be applied hot if you have experience doing such a thing. It has
teeth that sink into the insulation and tap the main conductor. It
tightens down with a socket wrench and the bolt that squeezes it is
insulated from the wiring so there is no exposure to hot wires during
the installation. Of course you would turn off the house main and
inverter disconnect during installation so no current is flowing. The
advantage here is not needing the utility to shut down the transformer
secondary, not having to wait for the service release inspection
(depending on relation to local AHJ) and not having to strip the main
conductors. Just run a 3/4" or 1" service riser with #6, put a
weatherhead on it, and go to a 3R 60 amp fused disconnect. See
240.21(B)(5)Outside Taps.
geoff at third-sun.com wrote:
>
> Wrenchtastic list members, What steps do you take (and what part of the
> NEC
> is referenced) when deciding to downsize a main breaker for busbar
> loading
> issues? My client is ready to "wing it" and slap a 150 amp breaker into
> the
> 200 amp panel, and this is an un-inspected job, but what about nuisance
> trips? sizing a service seams very elementary, but I would like to know
> the
> proper way to do it!
>
> Happy weekend to all and safe travels to the folks returning from San
> Jose
>
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
More information about the RE-Wrenches
mailing list