Backfeeding a 200 amp panel with an Outback 3048 [RE-wrenches]
Kurt Albershardt
info at es-ee.com
Wed Oct 18 02:29:01 EDT 2006
<x-flowed>
--On Tuesday, October 17, 2006 2:57 PM -0600 Ray Walters <walters at taosnet.com> wrote:
>
> The bussbar rating consideration should be based not on the breaker, but the max. possible backfeed the system can provide. (the array size)
The busbar rating is chosen based on the maximum load to which the busbar could be subjected (even if said condition is staggeringly unlikely.) Given sufficient branch circuit breakers and loads, the busbar could be asked to carry the combined load of both the utility feed and the inverter feed.
.
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
</x-flowed>
More information about the RE-Wrenches
mailing list