Ginormous battery rack [RE-wrenches]

Andrew Truitt atruitt at gmail.com
Mon Oct 2 15:41:57 EDT 2006


<x-flowed>

Thank you to everyone!  Lots of great advice as usual.

- Andrew


On 10/2/06, Ezra Auerbach, DragonSun Consulting <ezra at lasqueti.net> wrote:
>
> Hi all,
>
> Sorry for any confusion I may have caused. I do mean apply the
> Capacity divided by five (C/5) charge rate. Which  in these batteries
> (2KS33PS) equals 445 amps. The term "capacity" may cause confusion in
> this dicsussion. Here's why: we normally talk about battery capacity
> at the 72 hour rate (2225 amp hours for this model). This is
> appropriate for the usual rate of residential discharge and we are
> usually looking at storage capacity. However when looking at
> recharging the same battery the appropriate rate to refer to is the
> 20 hour rate. This is because the batteries will be charging faster
> than they were discharged hence more heat will be generated which in
> this case will actually hasten the charging process. The good news,
> is that the 20 hour rating for these batteries is 1766 amp hours
> hence we "only" need an initial charge rate of 353 amps.
>
> That's the problem with ginormous batteries, it takes a lot of
> current to properly recharge them. Most battery manufacturers who
> I've spoken to would like to see the C/5 rate and are thankful if the
> C/10 is a reality. Again for these batteries even the C/10 rate would
> be a charging system capable of 176 amps at 48 Vdc. Not an un-
> achievable charging system with an 8.5 kW array or a couple of large
> wind gennies, a few inverter/chargers or a combination of all. Much
> less than this much charging "umph" will eventually result in
> shortened battery life.
>
> Hope this clarifies.
>
> Ezra
>
>
> On 2-Oct-06, at 8:19 AM, Allan Sindelar wrote:
>
> >
> > Ezra,
> > Minor correction here with large consequences to the question at
> > hand...a
> > C/5 rate is "capacity at a five-hour rate", or 20% of the battery's
> > amp-hour
> > rating, rather than 5%.
> > Allan at Pos Energy
> >
> > ----- Original Message -----
> > From: "Ezra Auerbach, DragonSun Consulting" <ezra at lasqueti.net>
> >>
> >> I totally agree with Drake, your next challenge will be charging
> >> those batteries. You need an on-site ability to apply C5 (5% of the
> >> battery banks amp hour rating at the 20 hour rate).
> >
> >
> > - - - -
> > To send a message: RE-wrenches at topica.com
> >
> > Archive of previous messages: http://lists.topica.com/lists/RE-
> > wrenches/read
> >
> > List rules & how to change your email address: www.mrsharkey.com/
> > wrenches/etiquette.php
> >
> > Check out participant bios: www.mrsharkey.com/wrenches/
> >
> > Hosted by Home Power magazine
> >
> > Moderator: michael.welch at homepower.com
> >
> >
>
>
> - - - -
> To send a message: RE-wrenches at topica.com
>
> Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
>
> List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
>
> Check out participant bios: www.mrsharkey.com/wrenches/
>
> Hosted by Home Power magazine
>
> Moderator: michael.welch at homepower.com
>
>
>


-- 
Andrew Truitt
System Designer
Standard Solar Inc.
(301) 296 - 4373
andrewtruitt at standardsolar.com


- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read

List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php

Check out participant bios: www.mrsharkey.com/wrenches/

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com

EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com

For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------


</x-flowed>


More information about the RE-Wrenches mailing list