Cu to Al Splicing [RE-wrenches]

Mick Abraham mick at abrahamsolar.com
Wed Sep 6 08:21:58 EDT 2006


Hi, Wrenchies~

I'm a newcomer to the list and have mainly been lurking so far. In reply 
to Jeff's question below:

Consider using the ILSCO #CPM-3/0 "wire connector adapter" on the 
aluminum. See this @ ilsco.com This is a Noalox filled connector that 
crimps onto the cable much as with a battery lug, but the other end of 
the connector is a short bit of stranded tinned copper wire about the 
same size as #2 THHN. The connector comes with a plastic slip on 
insulation jacket but I suggest you instead use a big sleeve of glue 
filled heat shrink to seal the crimped connection. That would handle 
your aluminum degradation worries very completely, and it effectively 
"converts" your 3/0 aluminum into smaller gauge copper. 

Once you have "necked down" the aluminum to a size & material almost 
identical to your #2 copper cable, the Polaris type connector suggested 
by others would be smaller in size & less costly...or use a split bolt. 
Adapting the aluminum down in size and across into copper via the 
sealed/crimped connection makes the rest easy.

The ILSCO part mentioned above is 10 per box and may be hard to get in 
smaller quantity. Price it out at your local electrical supply house. 
You could then contact me off list if you only need one or two, as I 
have a partial box on hand.

Sorry if my name appears twice, but this is my first post to the list. I 
hope this will be helpful. Mick Abraham
 
Jeff Clearwater wrote:
> 
> Wrenches and Other assorted Hand Tools,
> 
> (So would that make Matt a Tourque wrench? : )
> 
> I need to splice 2 AWG Cu to 3/0 Al - potentially in an underground 
> pull box or outside above ground J-Box.  Can I hear folks preferred 
> methods?  A Cu/AL rated butt connector smeared with NoAlox and sealed 
> with 3M Mastic or Rubber Tape and then 88 tape would be my 
> inclination.  But 8 miles up a dirt road - 10 years from now I would 
> rather not have a callback!
> 
> Those wrenches with more tourque - or at least more experience - 
> please enlighten me!
> 
> Thanks!
> 
> Jeff C.
> 
> 
> -- 
> ~~~~~~~~~~~~~
> Jeff Clearwater
> Village Power Design
> Sustainable Energy & Water Solutions for Home & Village
> http://www.villagepower.com
> gosolar at villagepower.com
> NABCEP (tm) Certified Solar PV Installer
> 
> 530-470-9166
> 877-SOLARVillage
> 877-765-2784
> 72 Baker Rd.
> Shutesbury, MA 01072
> 425 Nimrod St.
> Nevada City, CA 95959
> ~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~`~



Abraham Solar Equipment
Pagosa Springs, CO
www.abrahamsolar.com


- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read

List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php

Check out participant bios: www.mrsharkey.com/wrenches/

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com

EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com

For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------





More information about the RE-Wrenches mailing list