Aluminum vs Copper? [RE-wrenches]
Ron Young
solareagle at solareagle.com
Mon Sep 4 02:55:43 EDT 2006
<x-flowed>
Thanks Hugh, Jeff, Chris and others for leading me down this path. If I
am understanding this correctly Hugh, and don't get too worried about
greater than 5% line losses at max output, and use aluminum with proper
precautions, then I can, say, use a 2/0 aluminum cable with a line loss
of about 8% (based on the derated 40 amps instead of 52) or a #2
copper, and not be too concerned? And if economics demanded I could
even go to a higher line loss bearing in mind that: "As loss increases,
the situation becomes much more complex, since more than 2 wires will
start to conduct at once during the changeover." as you state in your
answer to Paul Gipe on http://www.scoraigwind.com/CABLE/index.htm?
Honestly I don't pretend to know what that really means but if I can
get away with 8-10% without seriously compromising charging potential
then the wire cost savings will very pleasant.
2500 watt turbine - 48v - 300' wire run - 3 phase
Ron Young
On 3-Sep-06, at 2:59 PM, Hugh Piggott wrote:
>
>> Hi Ron,
>>
>> Basic 3-phase formula: P/V/1.73=I
>>
>> Or Power divided by Voltage divided my 1.73 = Amperage per leg (1.73
>> is the square root of 3).
>
> This formula is true when we are talking about a star connected supply
> with 48 volts on each phase relative to neutral. If we are talking
> about rms current in a wire feeding a rectifier with 48 volt DC output
> then the answer is very different. Rather than 1/1.73 (=0.58) it is
> closer to 0.8. The volt drop is therefore larger than a lot of people
> would assume. rms current in each of the 3 wires is about 0.8 (sq
> root of 2/3) times the DC current after the rectifier. 2500/48 is 52
> amps so I would reckon about 40 amps rms per wire. And you lose power
> in all three wires.
>
> There is some vagueness about the exact current factor because it does
> depend on source impedance and waveform, but the variation in the
> answer is not big. Anyone interested in the nitty gritty, check out
> http://www.scoraigwind.com/CABLE/index.htm
>
> Since most energy is delivered at less than 2500 watts it is not
> necessary to get in a big panic about losses over 5%. In high wind,
> the wind turbine alternator will very likely deliver much the same
> current anyway and become more efficient in the process so the loss is
> less than you would assume. (I guess the same reasoning applies to PV
> in a lot of cases.)
>
> Isn't copper getting expensive?
> --
> Hugh
>
> Scoraig Wind Electric
> http://www.scoraigwind.co.uk/
>
>
> - - - -
> To send a message: RE-wrenches at topica.com
>
> Archive of previous messages:
> http://lists.topica.com/lists/RE-wrenches/read
>
> List rules & how to change your email address:
> www.mrsharkey.com/wrenches/etiquette.php
>
> Check out participant bios: www.mrsharkey.com/wrenches/
>
> Hosted by Home Power magazine
>
> Moderator: michael.welch at homepower.com
>
>
>
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
</x-flowed>
More information about the RE-Wrenches
mailing list