I guess my point was not clear.

Quoting my 2002 NEC Handbook note on 250.97 "Bonding around prepunched 
or eccentric knockouts is not required if the enclosure containing the 
knockouts has been tested and listed as suitable for bonding."

This goes back to my note on UL listing. It seems that while you still 
may have a question regarding the code, your real question goes to the  
listing of the disconnect.  Are the knockout in your disconnect tested 
and listed as suitable for bonding.


Mark Frye