Concentric knockouts on circuits over 250 volts [RE-wrenches]
William Miller
wrmiller at charter.net
Mon Aug 28 03:26:14 EDT 2006
<x-flowed>
At 08:13 PM 8/27/2006, you wrote:
Bob-O:
I do not see where the citation excludes conduits that carry a separate
equipment grounding conductor. We always pull a ground, but it connects to
the module frames and does not bond the conduit at either end. The logic
behind this? My guess: A nick in the insulation of a conductor carrying
voltage could energize the conduit, I guess.
If you could point out where the citation excludes conduit in the situation
you describe, I could win a pissing match with a local inspector.
William
>William
>If I read this right, this only applies to situations where one is
>using the EMT or the like as the grounding conductor. Where one
>carries a grounding conductor from the PVs down to the DC disco and
>it is bonded to all the metal boxes using a lay-in lug or the like, I
>don't see the need for the bonding bushings. Just my thoughts, I
>could be wrong.
>Bob-O
>On Aug 27, 2006, at 12:18 PM, William Miller wrote:
>
>>
>>Friends:
>>
>>It has come to my attention that bonding bushings are required in
>>our DC feeder conduit where it enters the DC disconnect via
>>concentric knockouts per NEC:
>>
>>250.97 Bonding for Over 250 Volts.
>>For circuits of over 250 volts to ground, the electrical continuity
>>of metal raceways and cables with metal sheaths that contain any
>>conductor other than service conductors shall be ensured by one or
>>more of the methods specified for services in 250.92(B), except for
>>(1).
>>Exception: Where oversized, concentric, or eccentric knockouts are
>>not encountered, or where a box or enclosure with concentric or
>>eccentric knockouts is listed for the purpose, the following
>>methods shall be permitted:
>>(a) Threadless couplings and connectors for cables with metal sheaths
>>(b) Two locknuts, on rigid metal conduit or intermediate metal
>>conduit, one inside and one outside of boxes and cabinets
>>(c) Fittings with shoulders that seat firmly against the box or
>>cabinet, such as electrical metallic tubing connectors, flexible
>>metal conduit connectors, and cable connectors, with one locknut on
>>the inside of boxes and cabinets
>>(d) Listed fittings that are identified for the purpose
>>
>>
>>250.92 Services.
>>(B) Method of Bonding at the Service. Electrical continuity at
>>service equipment, service raceways, and service conductor
>>enclosures shall be ensured by one of the following methods:
>>(1) Bonding equipment to the grounded service conductor in a manner
>>provided in 250.8
>>(2) Connections utilizing threaded couplings or threaded bosses on
>>enclosures where made up wrenchtight
>>(3) Threadless couplings and connectors where made up tight for
>>metal raceways and metal-clad cables
>>(4) Other approved devices, such as bonding-type locknuts and bushings
>>Bonding jumpers meeting the other requirements of this article
>>shall be used around concentric or eccentric knockouts that are
>>punched or otherwise formed so as to impair the electrical
>>connection to ground. Standard locknuts or bushings shall not be
>>the sole means for the bonding required by this section.
>>
>>
>>
>>William Miller
>>
>>
>>__________________________________________________________________
>>William Miller
>>Miller Power and Communications
>>Voice :805-438-5600 Fax: 805-438-4607
>>email: wrmiller at mpandc.com
>>http://mpandc.com
>>License No. C-10-773985
>>_____________________________________________________________
>>Check out our latest project at http://mpandc.com/case_studies/
>>pv_school/pv_school.html
>>
>>- - - -
>>To send a message: RE-wrenches at topica.com
>>
>>Archive of previous messages: http://lists.topica.com/lists/RE- wrenches/read
>>
>>List rules & how to change your email address: www.mrsharkey.com/
>>wrenches/etiquette.php
>>
>>Check out participant bios: www.mrsharkey.com/wrenches/
>>
>>Hosted by Home Power magazine
>>
>>Moderator: michael.welch at homepower.com
>>
>
>
>- - - -
>To send a message: RE-wrenches at topica.com
>
>Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
>
>List rules & how to change your email address:
>www.mrsharkey.com/wrenches/etiquette.php
>
>Check out participant bios: www.mrsharkey.com/wrenches/
>
>Hosted by Home Power magazine
>
>Moderator: michael.welch at homepower.com
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
</x-flowed>
More information about the RE-Wrenches
mailing list